Multiple UF cables in one LB box

Reply

  #1  
Old 07-21-16, 06:21 AM
Member
Thread Starter
Join Date: Jul 2016
Location: USA
Posts: 2
Multiple UF cables in one LB box

I'm running three different branch circuits from a single subpanel, two 20 amp and one 15 amp. I'm wondering how to get them outside the building.
1) Can I use a single LB box?
2) If so, I'd need a one inch LB, I think. I don't see any junction boxes with a knockout that big. The cables will only be going about 2 feet to the panel, so can I just bring them out of the LB and directly to the panel if they're properly supported?
3) If not, can I use three 1/2 inch LB boxes?
 
Sponsored Links
  #2  
Old 07-21-16, 07:38 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,597
Likes Received: 13
Best practice is to use single conductor wires not cable if this will be continuous conduit. If they are to a single building you can only have one circuit to that building. If it already has a circuit then you can replace that circuit but you can't add another circuit.
 
  #3  
Old 07-21-16, 07:50 AM
Member
Thread Starter
Join Date: Jul 2016
Location: USA
Posts: 2
Oh, I see I forgot to mention I'm running UF cable for the underground feed. The UF will come up to the LB in conduit, then enter the building.
 
  #4  
Old 07-21-16, 10:42 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 50,967
Likes Received: 155
Technically you're running three circuits in UF and then you're using a short piece of conduit from the ground up and in to the back of a sub panel. That would be called sleeving the cables.

A single 1" or 1-1/4" conduit and LB would be ok. 3/4" would be too small.
 