Arc Fault problems.

Hello all. My home has developed what appears to be a ground fault. Location and circuit load - Master bath lighting and exhaust fans, master bedroom fan/light combo, and living room fan/light combo, (no wall outlets). Brief history - Two months ago the breaker would trip once a month, we thought it was just over load. Then it would trip when any switch was operated. I thought it was just an old or weak breaker, so I replaced it. Still had the same problem. I removed all the switch from the wall (5) and the breaker still trips itself.

I am asking for help in locating where and why this happened. The house has not been remolded, no bad weather, and nothing has changed in the house. The problem went from intermittent to permanent.

Please help with any suggestion of what to do next.

Thank you.

J
 

Last edited by pcboss; 07-22-16 at 08:27 AM. Reason: changed title, was Ground Fault
Sponsored Links
  #2  
Old 07-21-16, 05:53 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
To isolate the problem you need to remove all equipment and fixtures from the circuit and test. If it no longer trips you need to add back each piece of equipment one at a time till the circuit trips. In cases such as switches after removal you need to bypass by connecting the switch wires together.
 

Last edited by ray2047; 07-22-16 at 09:34 AM. Reason: Re read the question.
  #3  
Old 07-21-16, 09:22 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,608
Received 339 Votes on 317 Posts
Yeah.... a lot of motors if on a GFI. There's a good chance of a neutral to ground leak. That would cause the GFI to trip even if the device wasn't running.

Either way.... with or without a GFI.... Ray's method is probably the best way to find the problem.
 
  #4  
Old 07-22-16, 04:28 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,933
Received 54 Votes on 47 Posts
If this is home is 2002 or newer it is likely an AFCI breaker.
 
  #5  
Old 07-22-16, 05:51 AM
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 1,176
Received 28 Votes on 24 Posts
You could have a overcurrent or short (possibly intermittent) condition. Both require some knowledge of electrical troubleshooting.
Open each electrical box for the switches and fan/lights and make sure all screw connections are tight and wires in wire nuts are secure. If all are OK and problem still exists, buy or rent a AC ammeter (at least 30 A) to check for overcurrent condition. Place AC ammeter in series with the offending breaker. With all switches OFF, ammeter should read 0 A. With all three switches ON, the AC ammeter is indicating the RMS amps. The value should be less than the breaker amp rating. If not , insure the wire size on the breaker is large enough for the next higher rated breaker and replace breaker.
If the AC ammeter does not read 0A with all three switches OFF, there is a short somewhere in the AC source wiring and troubleshooting to isolate the source of the short will be required.
 
  #6  
Old 07-22-16, 08:02 AM
Member
Thread Starter
Join Date: Jul 2016
Location: USA
Posts: 8
Received 0 Votes on 0 Posts
No. The GFCI's are on a different circuit for all the 110 outlets.

And thank you for the reply. I will start removing all the equipment.

I thought that by removing the switches it would have automatically taken the equipment out of the circuit back to breaker. Is this not true. The living room fan/light combo has always had problems not working properly! As well I do not understand why it on this (master bath/bedroom) circuit
 
  #7  
Old 07-22-16, 08:12 AM
Member
Thread Starter
Join Date: Jul 2016
Location: USA
Posts: 8
Received 0 Votes on 0 Posts
Correct, it is an AFCI breaker
 
  #8  
Old 07-22-16, 08:17 AM
Member
Thread Starter
Join Date: Jul 2016
Location: USA
Posts: 8
Received 0 Votes on 0 Posts
I don't believe my typical multi-meter is rated for 30amps, so I will get a new one that is.
 
  #9  
Old 07-22-16, 08:25 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,911
Received 24 Votes on 20 Posts
It does not sound like you need to check for overloads.I suspect there is a loose connection, possibly at the breaker.
 
  #10  
Old 07-22-16, 08:39 AM
Member
Thread Starter
Join Date: Jul 2016
Location: USA
Posts: 8
Received 0 Votes on 0 Posts
Before I start to dismantle the house I did a quick continuity check at one of the switches. I get continuity between ground and both the hot and neutral wires. When they built they sprayed the rooms it made all the wires white, but after get the paint off they are all black which I am not familiar with as typical romex.

Any ideas?
 
  #11  
Old 07-22-16, 08:43 AM
Member
Thread Starter
Join Date: Jul 2016
Location: USA
Posts: 8
Received 0 Votes on 0 Posts
Thank you pcboss, I will get back into the breaker box, check, and even swap out the breaker again with one that is currently working.
 
  #12  
Old 07-22-16, 09:03 AM
pugsl's Avatar
Forum Topic Moderator
Join Date: Mar 2008
Location: Raleigh, NC
Posts: 8,407
Received 19 Votes on 18 Posts
You have fan problems I would check connections there first.
 
  #13  
Old 07-22-16, 09:21 AM
Member
Thread Starter
Join Date: Jul 2016
Location: USA
Posts: 8
Received 0 Votes on 0 Posts
Already pulled the connection on one fan. Going to take the next one apart.

I just got done double checking the breaker box, swapped the breakers, etc. All good, except 1.8 ohms common to ground. Going to go check the other fan.

Thank you all, I will report back.
 
  #14  
Old 07-22-16, 11:12 AM
Member
Thread Starter
Join Date: Jul 2016
Location: USA
Posts: 8
Received 0 Votes on 0 Posts
It was in the bedroom ceiling fan lighting short.

Thank you all for your help.

J
 
  #15  
Old 07-22-16, 11:58 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Glad you got it. Thanks for letting us know the outcome.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: