3 wire to 4 wire conversion for Hot Tub

I'm installing a new hot tub, replacing and existing one that was wired with only 3 wire (two hot/one ground). When determining if I was going to replace the entire line, I realized the main panel is still single ground/neutral bar (grounds and neutrals are all wired to the same bar). Since the main panel is shared ground/neutral, is it still required to run a dedicated ground all the way to the panel, or can I marry the ground to the neutral at the tub? (also, read conflicting opinions on grounding rod, any thoughts there assuming I use the 3rd wire going to the panel as the neutral?)
 
  #2  
Old 08-08-16, 03:43 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,581
Received 13 Votes on 11 Posts
Since the main panel is shared ground/neutral, is it still required to run a dedicated ground all the way to the panel
No you need 4-wire (H,H,N,G) to the hot tuber. No ground rod required but if on a concrete slab you may need bonding to the rebar in the slab.
 
  #3  
Old 08-08-16, 03:46 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 62,651
Received 1,611 Votes on 1,483 Posts
Welcome to the forums.

A true 240v hot tub only requires two hot wires and ground.
A 120/240v hot tub requites a separate neutral or four wires.
 
  #4  
Old 08-08-16, 07:17 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,259
Received 114 Votes on 99 Posts
A ground rod will do nothing at the tub and is not required.
 
 