Can I put a 60 amp breaker in this 30 amp slot?
Old 09-24-16, 08:11 AM
H
Here is the slot.
I pulled this 30 amp breaker out of it.
My goal is to install a Rheem EcoSense RETE-13 - 13kW 1.97 GPM Tankless Electric Water Heater.
This:
Square D Homeline 60 Amp Two-Pole Circuit Breaker-HOM260CP - The Home Depot
has two switches, unlike the 30 amp one I pulled out. I cannot tell if the Rheem requires the two-switch one, and if so, can I put a two-switch one in the slot the single-switch one came out of?
The 30 amp breaker was for a tank water heater. Also, the existing wire is 10/2, ground-type NM, 600V. The Rheem requires "240-Volt electrical service." Am I ok using the existing wire for that?
This seemed so simple when I first looked into it.
Old 09-24-16, 08:24 AM
chandler's Avatar
Received 6 Votes on 6 Posts
Google photos is not opening. Try this: http://www.doityourself.com/forum/el...your-post.html
You cannot increase the overcurrent protection on your current wiring. 10 gauge wire is dictated for a 30 amp circuit. If the breaker you pulled only occupied one slot, it is 120 volts. Your unit requires 240 volts. Why do you want to install a 60 amp breaker? Does the manufacturer call for it?
Old 09-24-16, 08:28 AM
ray2047's Avatar
Received 13 Votes on 11 Posts
Google is not a good choice for images. Maybe you can see it. No one else can. http://www.doityourself.com/forum/li...rt-images.html
The slot doesn't care what size breaker you put in as long as it doesn't exceed the buss rating. You can only use a Square D breaker in a Square D panel. You need at least #6 wire for a 60 amp breaker.
Old 09-24-16, 08:56 AM
chandler's Avatar
I think the OP is thinking of "doubling" the capacity of the single 30 amp breaker. We'll see when he returns with pictures.
Old 09-24-16, 09:03 AM
Tolyn Ironhand's Avatar
Received 252 Votes on 220 Posts
The answer is no. Your panel is a Square D QO panel. This is the breaker you need: Square D QO 60 Amp Two-Pole Circuit Breaker-QO260CP - The Home Depot Even though it only has one handle it is a two pole breaker that will give your heater 240 volts it needs.
The existing wire is not large enough for 60 amps. You will need to run a new 6-2 with ground cable off the new 60 amp breaker to your new heater.
Heater specs: 13kW water heater requires a 240-Volt electrical service, a dedicated 60 Amp breaker and 6-Gauge copper wiring From here: Rheem EcoSense RETE-13 - 13kW 1.97 GPM Tankless Electric Water Heater-RETE 13 - The Home Depot
Old 09-24-16, 10:39 AM
H
Tolyn Ironhand, you beast. Thank you. Exactly what I needed to know.
Old 09-24-16, 10:46 AM
H
I just can't thank you enough for your reply. All the info I needed, so quick, so thorough. Thank you!
Old 09-24-16, 12:10 PM
H
30 amp breaker and 10/2 wire ok for this Rheem water heater?
The breaker is on a Square D QO panel. It is a large (double the width of others on panel) breaker with one switch. Here is a pic.
The heater I have in mind is this one:
Rheem Performance 38 Gal. Short 6 Year 3800/3800-Watt Elements Electric Water Heater with Blanket-XE38S06ST38U1 - The Home Depot
It says it's 3800 watts and "Requires a 240-Volt connection for installation."
In the manual there is a table that says for 4000 watts, 10 guage wire is correct, but a 25 amp breaker is needed. That's all I could find to go on, and I don't know if that means using a 30 amp breaker for this would instantly burn my house to the ground, or if it would simply be adequate. The existing breaker and wire were used for the old heater I am replacing, curse its soul.
Old 09-24-16, 12:21 PM
With that heater you could use the existing wire but change the breaker to a QO 25 amp breaker. Here is what you need but you will need to order it as they will not have it in stock.: Square D QO 25 Amp Two-Pole Circuit Breaker-QO225CP - The Home Depot
IMO - A 20 amp breaker should also work as 3800 watts / 240 volts is 15.8 amps.
I think this is a better option then the tankless IMO. However, if you have the room, I would recommend getting a heater with larger elements for faster recovery time and you would not need to modify the electrical at all. Here is a good option similar to what you are looking at but is a bit cheaper: Rheem Performance 40 Gal. Medium 6 Year 4500/4500-Watt Elements Electric Water Heater-XE40M06ST45U1 - The Home Depot
Old 09-24-16, 02:54 PM
ray2047's Avatar
Hundy please stop starting multiple threads on the same subject. I have merged your threads. A bit confused by the second thread you started. Are you now changing what you are going to install?
Old 09-24-16, 04:57 PM
H
Thank you AGAIN!! Your expertise is deeply appreciated.
Also your recommendation for a different heater looks good to me and I do indeed have the room.
Honestly I was only going for the shorter one to get out of having to rent a truck to haul it. I have heard they ride ok on their sides but seems risky.
BTW it looks like I accidentally used the same title as my previous post and I'm sorry for any confusion that caused.
Old 09-24-16, 05:02 PM
H
Sorry about that! Yes I am indeed considering an additional heater, so I thought I would start a new thread, even though the question involves the same breaker panel.
Old 09-26-16, 09:07 AM
I
Received 44 Votes on 42 Posts
BTW, you might have already bought it, but they do ride just fine on their side as long as the thermostat/control side is up so as to not get crushed.