Can I install a 15-amp GFCI outlet in the bathroom?

Hi guys, I'd like to install an outlet in a bathroom, which will be just below a light switch, which is on a 15amp circuit. I'm planning to connect a new piece of cable in the box for the switch and drop it behind the wall, into the new box for the outlet. Since it's a bathroom I'm getting a GFCI outlet, however I'm finding mixed information about whether it can be on a 15amp circuit. At the same time you can obviously buy a 15amp GFCI outlet. I've noticed that all other GFCI outlets in my house (including another one in the same bathroom) are on 20amp *dedicated* circuits. Will I be doing something that's not by the code if I were to install a 15amp outlet there? And if I can do it, how can I make sure that I can add another receptacle to this particular circuit (where the lights are)? Thanks in advance.
 
Sponsored Links
  #2  
Old 10-09-16, 02:30 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
I'd like to install an outlet in a bathroom, which will be just below a light switch, which is on a 15amp circuit.
First you need to open the switch box and see if you have power at the switch. Many older homes use switch loops and there is no neutral at the switch so no power for a receptacle. If the switch box has only two wires, a black and white, connected to the switch then there is no neutral for a receptacle.

As to can you have a GFCI 15 amp circuit the answer is yes if it is in addition to the required dedicated 20 amp receptacle circuit.

Note please fill in your location in your profile. In the U.S. you can in most cases use a 15 amp GFCI receptacle on a 20 amp circuit. In Canada you can.
 
  #3  
Old 10-09-16, 08:57 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,144
Received 84 Votes on 72 Posts
The NEC requirement is for a 20 amp circuit to serve the bathroom receptacle (s). A 15 amp gfi receptacle can be used as it is two receptacles.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: