Wiring gauge or circuit breaker- Which defines the circuit?

I think I know the answer, but I would like reassurance. I have a home built in 1988. The home's breaker box contains 15 and 20 amp breakers. About a 50/50 ratio. I am changing some kitchen lighting. In opening the 4" j-box I noted what I think was 12 gauge wire. When I went to the breaker box the circuit breaker was a 15 amp breaker. I thought 12 gauge was normally for 20 amp circuits. I cannot understand why an electrician would use it for a 15A circuit.

Can someone explain?
 
Sponsored Links
  #2  
Old 10-12-16, 07:12 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,123
Received 71 Votes on 61 Posts
The minimum gauge for a 20 amp general circuit is #12 and #14 for a 15 amp circuit. Larger csizes of wire can be instaĺled.

Perhaps there is #14 somewhere in the circuit.
 
  #3  
Old 10-12-16, 07:13 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
When I went to the breaker box the circuit breaker was a 15 amp breaker. I thought 12 gauge was normally for 20 amp circuits.
It is but there is nothing wrong in using a larger size.
I cannot understand why an electrician would use it for a 15A circuit
It is what was on the truck or some sections of the circuit has #14.
 
  #4  
Old 10-12-16, 08:45 AM
G
Member
Join Date: Nov 2007
Location: MI
Posts: 2,631
Received 1 Vote on 1 Post
...or some sections of the circuit has #14.
Perhaps there is #14 somewhere in the circuit.
Is that allowed by code? It seems misleading to use 12 at the panel, then switch to 14 in a junction box. If I were to make changes downstream I would base my wire & load choices by what I see in the panel.
 
  #5  
Old 10-12-16, 09:35 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,123
Received 71 Votes on 61 Posts
As long as the smallest conductor is protected it is allowed. It may not be best practice for the reason you stated.
 
  #6  
Old 10-14-16, 02:05 AM
S
Member
Thread Starter
Join Date: Feb 2011
Location: United States
Posts: 221
Received 0 Votes on 0 Posts
Sorry for the late reply. I got no alert that replies were made and forgot about my post.

So, I think I get it. It was OK for the electrician to use 12 ga wire on a 15A circuit. Some overkill, but OK. I find the stuff stiff and difficult to work with. I don't think I would have used it when it was not required.

More confusing yet. In a couple cases I see both 12ga and 14ga used on the same 15A circuit. Based on comments here it is still OK. Just confusing for a beginner like me.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: