Wiring bypass humidifier to furnace

I installed a bypass humidifier last season, and installed a receptacle for it. Iím upgrading my bathroom, and need the circuit.

I want to wire it so it only comes on when the heat turns on, not with the fan. The wife leaves the fan on all the time.

Itís a Honeywell HE120, came with a transformer - labeled ĎPrimary - 120VAC 60Hz; Secondary 24VAC 0.416A 10VAí each connects to the humidistat

The furnace is a Lennox Pulse, circa 1985. Below is the wiring diagram. Any help would be great!!

Name:  IMG_8647.jpg
Views: 1288
Size:  49.1 KB
 
Sponsored Links
  #2  
Old 10-25-16, 05:43 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,652
Received 517 Votes on 487 Posts
What is the part number on that diagram ?
The board limits the size of the pics posted. There is not enough definition for me to help you.

Just curious.... when was the last time you had that furnace checked out ?
They've had major problems with the heat exchangers cracking. Some major recalls too.
It should be checked every year at its age.

Also.... a CO detector is a good investment too.
 
  #3  
Old 10-25-16, 06:52 PM
Member
Thread Starter
Join Date: Mar 2014
Location: USA
Posts: 141
Received 0 Votes on 0 Posts
I have a CO detector. HVAC guy suggested it when we had some new ducts/returns installed. He checked it out then. It was about 2-3 years ago.

Hereís a link for better photos, i hope

https://goo.gl/photos/TNacxfNN41aKPZeq5
 
  #4  
Old 10-25-16, 11:57 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,652
Received 517 Votes on 487 Posts
I would continue to use that transformer and a 24vac relay for control.
The relay would be controlled by the W terminal of the thermostat.
 
  #5  
Old 10-26-16, 12:11 AM
Member
Thread Starter
Join Date: Mar 2014
Location: USA
Posts: 141
Received 0 Votes on 0 Posts
I donít fully understand your response.

Is there a way to lose the transformer and power the humidifier from the furnace? Itís just a small motor that turns a drum.
 
  #6  
Old 10-26-16, 12:40 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,652
Received 517 Votes on 487 Posts
It wouldn't just be powered from the furnace. It would get it's 24vac from the furnace thru the thermostat. It's one way to wire a humidifier. Puts a heavier than normal load on the thermostat.

The diagram is the connection. Since it's 24vac.... there is no particular order.
W and C are where your thermostat wires connect to the furnace control board.

Name:  HE_custom_wiring.JPG
Views: 2671
Size:  29.8 KB

Looking at your new pictures..... I see a custom relay sitting right next to the stat connections.
 
  #7  
Old 10-26-16, 06:12 AM
Member
Thread Starter
Join Date: Mar 2014
Location: USA
Posts: 141
Received 0 Votes on 0 Posts
There is no solenoid valve. It has a float that releases water. Just a small motor that turns the drum. I'm not trying to put any extra strain on my ancient system. I'm pretty sure my wife would rather have heat than humidity. Could this damage the system at all?

Which it the common terminal? Would it be the 'T'?
 

Last edited by MIdCityChef; 10-26-16 at 06:28 AM.
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: