Hot/Neutral Continuity?

I just installed a new outlet for the closet, and branched it off the one on the other side of the wall. Easy job.

Except, once I go to check continuity after boxing it all back up, I get 14.3 ohms across hot/neutral, hot/ground, and neutral/ground. I worked backward to see if I did anything, but the insulation is all in fine shape and my connections are good.
I tore my hair out for a little bit, and then since it is an AFCI breaker, I took a deep breath and flipped it anyway. My test lamps all lit up just fine and the breaker stays put.

I have never seen this, is it possible this is the Siemens AFCI outlet is giving me false continuity readings?
 
Sponsored Links
  #2  
Old 11-06-16, 03:54 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,067
Received 75 Votes on 69 Posts
Except for guru experts, it is not useful to touch one meter probe to a hot terminal and the other probe to the neutral terminal and try to do a continuity test.

Don't forget, never test for resistance or continuity until after you turn off the power.

For now assume that the 14.3 ohm reading you got means absolutely nothing.

Yes you should get about 120 volts from hot to neutral with or without a hair dryer plugged in and switched on. (You can measure at the other half of your duplex receptacle; voltage may vary a coupl'a volts.)
 
  #3  
Old 11-06-16, 03:59 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 58,513
Received 1,030 Votes on 956 Posts
Welcome to the forums.

Thank goodness the power was off when you used the ohms/continuity scale or you could have destroyed your meter.

You cannot measure resistance into a GFI or AFCI device. If you think you have a short in a circuit and you want to use an ohmmeter.... the wiring must be removed from the breaker/protective device for any type of meaningful measurement.
 
  #4  
Old 11-07-16, 02:14 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 43 Votes on 41 Posts
The continuity reading of 14 ohms means that there is something plugged in and turned on in that circuit, most likely a transformer or power supply of an always-on device like a clock radio or TV.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: