Feeder wire for sub panel
Old 11-07-16, 03:36 PM
if you were putting a 100 amp subpanel 80 ft away from the main would you use 2 awg copper?
I assume the neutral has to be the same size?? would you just drive a new ground rod to save
running a ground??
Can you find 2 awg for 1.25 a ft??
Old 11-07-16, 04:10 PM
Received 1,029 Votes on 955 Posts
Depending on where the subpanel is going you MAY need a ground rod but you DO need four wires. Two hots, neutral and a ground wire. #2 THWN copper from the depot is about $1.50'.
Old 11-07-16, 04:14 PM
P
Received 93 Votes on 73 Posts
Actually I'd run three #1 aluminum XHHW-2 and a #6 aluminum XHHW-2 for the EGC for 100A. You need 2 ground rods at the detached structure for the electrode system plus the EGC back to the house main panel.
Edit the #1 aluminum is about $0.43 a foot, so for total of the four conductors you are looking at less than $1.60 a foot. This wire does need to be in conduit.
See here.. https://www.wireandcableyourway.com/XHHW-2/
USE-2/RHH/RHW-2, is direct bury.
See here... https://www.wireandcableyourway.com/...HW-2-Aluminum/
Old 11-07-16, 05:49 PM
ray2047's Avatar
Received 13 Votes on 11 Posts
Depending on the load you may not need to supply a "100 amp" subpanel with 100 amps. For instance most garages are fine on 60 amps or less. What is the purpose of the subpanel?
Old 11-08-16, 05:15 PM
alum will be ok. and 60 amps is enough too. so 100 ft would be about 1500 for wire.
Way more than 30 years ago.insane.
Old 11-08-16, 05:53 PM
P
1500? It will be about $150-160 for 100ft.