NMB in conduit
Old 11-13-16, 08:49 AM
Grady's Avatar
Received 23 Votes on 21 Posts
NMB in conduit
I want to run a 20A circuit from one shed to another. Since I have a lot of 12/2 G romex left from another project, I'd like to run it in PVC conduit underground to the second shed. Is this legal?
Old 11-13-16, 08:53 AM
Received 1,046 Votes on 970 Posts
No can do. NM-b is not rated for wet use. Anything outside...even in conduit... is considered wet.
Old 11-13-16, 09:29 AM
Grady's Avatar
Thanks Pete. I thought that's what I remembered but wasn't sure. Indoors is ok but not outdoors?
Old 11-14-16, 08:41 AM
I
Received 43 Votes on 41 Posts
NM is OK in a "normally dry" environment per code. It also requires "protection from damage" which is subjective, but may or may not be OK in your shed depending on the construction and what it's used for. Underground or wet location you'd need UF cable, but also still needs to be protected.
Old 11-14-16, 04:41 PM
Grady's Avatar
I'm going to get some THWN & run it in PVC conduit. Once it gets inside a box in the shed I'll switch to romex.
Old 11-14-16, 06:22 PM
ray2047's Avatar
Received 13 Votes on 11 Posts
That would be a good plan.