Hi all,
My wife and I bought a home that primarily has two-prong outlets. Down the road I plan to rewire the house and add a ground to every outlet, but in the meanwhile I'm simply replacing certain outlets with GFCIs as a stopgap.
On a box I replaced the other day, I'm experiencing a strange thing. I identified the positive/negative leads, and also made sure to get the line/load connections right. When I tested the outlet before pushing it all the way in the box, just to be double check that it all worked, everything worked fine. But when I pushed the receptacle into the box, every outlet further down the circuit from this receptacle turned off. I can reproduce this issue simply by pulling the receptacle out of the box a bit (everything down-circuit turns on again) and then pushing it back in (everything down-circuit turns off).
My best guess is that somehow the wires are getting kinked and causing this disruption. Has anybody seen a similar issue, or does anyone have an idea what might be causing this? Thanks!
My wife and I bought a home that primarily has two-prong outlets. Down the road I plan to rewire the house and add a ground to every outlet, but in the meanwhile I'm simply replacing certain outlets with GFCIs as a stopgap.
On a box I replaced the other day, I'm experiencing a strange thing. I identified the positive/negative leads, and also made sure to get the line/load connections right. When I tested the outlet before pushing it all the way in the box, just to be double check that it all worked, everything worked fine. But when I pushed the receptacle into the box, every outlet further down the circuit from this receptacle turned off. I can reproduce this issue simply by pulling the receptacle out of the box a bit (everything down-circuit turns on again) and then pushing it back in (everything down-circuit turns off).
My best guess is that somehow the wires are getting kinked and causing this disruption. Has anybody seen a similar issue, or does anyone have an idea what might be causing this? Thanks!
#3
Member
Join Date: Nov 2016
Location: USA
Posts: 2
Received 0 Votes
on
0 Posts
sounds like a bad connection... a wire is loosing contact when you push the box in.
a "kink" will not cause that, unless there is a break in the copper inside the insulation that you cannot see. when pulled out, the copper is in contact, but then when you push it in, the contact is lost. This is dangerous. An arc can occur and set things on fire.
or is the gfci tripping when you push it into the box?
a "kink" will not cause that, unless there is a break in the copper inside the insulation that you cannot see. when pulled out, the copper is in contact, but then when you push it in, the contact is lost. This is dangerous. An arc can occur and set things on fire.
or is the gfci tripping when you push it into the box?
#5
Member
Thread Starter
Join Date: Nov 2016
Location: United States
Posts: 4
Received 0 Votes
on
0 Posts
Thanks for your responses and follow-ups! Here are answers to your questions/responses.
1. ray2047, yes, they are cloth covered wires.
2. venison, the GFCI does not trip. I simply lose power to all receptacles "downstream" (the load side)
3. pcboss, thanks for your keen eye and clarification. I should have written hot/neutral.
Still experiencing the problem. Finally got some time today to play around with it; will post an update afterwards. Thanks!
1. ray2047, yes, they are cloth covered wires.
2. venison, the GFCI does not trip. I simply lose power to all receptacles "downstream" (the load side)
3. pcboss, thanks for your keen eye and clarification. I should have written hot/neutral.
Still experiencing the problem. Finally got some time today to play around with it; will post an update afterwards. Thanks!
#7
Member
Thread Starter
Join Date: Nov 2016
Location: United States
Posts: 4
Received 0 Votes
on
0 Posts
ray2047, when I do that everything works fine. In fact, I can identify a "point of no return" – until the receptacle is about 75% in the box, it works fine. As soon as I push it in the last 25% to screw it tight, that's when I lose power downstream.
Is there a fix for old insulation, short of replacing the wire? Would it be a safety hazard to wrap electrical tape around each wire?
Thanks!
Is there a fix for old insulation, short of replacing the wire? Would it be a safety hazard to wrap electrical tape around each wire?
Thanks!
#9
I can reproduce this issue simply by pulling the receptacle out of the box a bit (everything down-circuit turns on again) and then pushing it back in (everything down-circuit turns off).
The power comes on and off without tripping the breaker or the GFCI, that means a loose wire.
#10
probably a loose connection within a wire nut.
#12
Turn breaker off, remove wires from outlet, carefully wiggle wires one at a time. if one bends easy there will be a break in the wire. This has a 30 to 40 % chance of finding the problem.