Exclamation Neutral to ground shows voltage.

I'm stumped on my circuit, 120v 15a. At the outlets, I'm getting an open ground reading using the three light outlet tester. Doing a voltage test at the outlets I get the following: Hot-Neutral = 124v; Hot-Ground = 47v; Neutral-Ground = 53v. I can't figure out what's going on. At the panel, everything tests out fine. Help!
 
Sponsored Links
  #2  
Old 12-10-16, 12:09 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
You need to check all the ground connections on the circuit. If you have old style BX with no bonding strip that could be a cause also.
 
  #3  
Old 12-10-16, 01:41 PM
K
Member
Thread Starter
Join Date: Apr 2014
Posts: 11
Received 0 Votes on 0 Posts
Just to clarify, this a new house with new Square D panels. I've added about 8 circuits as I'm finishing the walkout level. Everything else works fine. It's just this one circuit.
 
  #4  
Old 12-10-16, 01:52 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,679
Received 1,173 Votes on 1,088 Posts
Ok... so you more than likely have NM-b cable in place.

That means you will need to identify everything on that problem circuit and go from device to device to find the issue.

I start at the device/location closest to the panel as that's where the circuit originates from and should be ok..... and work away from that point.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: