Ground bar on sub panel
Old 12-10-16, 09:57 PM
V
Hey guys I had a sub panel put in my house and read that you have to keep neutrals and grounds on separate bars. Just wanted to make sure I have to right bar before I hook anything up. Is this the ground bar?
Old 12-10-16, 10:29 PM
Received 597 Votes on 562 Posts
That is a ground bar since it's connected to the incoming ground wire and bonded to the metal box.
There should be an isolated bus bar fed with a white wire for neutral..... correct ?
Old 12-10-16, 10:38 PM
V
Yes, I think so. Here is a photo of the other side. I also have a quick question. The boxes I bought for my receptacles have ground screws on them as well. Do I use both the ground screw and the ground bar, just the bar, or both?
Old 12-10-16, 10:45 PM
That's the neutral bar hiding in the darkness on the left side.
When you wire using metal boxes...... the ground gets connected to the box with a green ground screw and then connects to the receptacle.
Old 12-10-16, 10:55 PM
V
Ah, I see. Thank you for the help. So connect the ground in the receptacle box on the green screw and then pigtail together the ground wire and connect to the receptacles in the box and on the other end stick the ground on the ground bar? Would that be good?
Old 12-10-16, 11:54 PM
Yup.... sounds like a plan.
There are many ways of connecting the grounds in a box. I like to leave one ground wire from one cable long. I wrap it around the green screw, twist the other grounds to it and then use a green wire nut. The green wire nut combines the grounds and allows the long one to connect to the device.