Wiring up 24vac relay "and"/ "or" circuit

I am trying to energize one "fan in a can" circuit to 2 dryers. It's easy enough to connect a 24vac relay to either of the dryer's blower contactor in order to energize the fan, so that if either dryer is running it will fire it's relay. How can I wire this so that if both dryer's are running at the same time they are not both trying to energize the fan at the same time?
 
Sponsored Links
  #2  
Old 12-14-16, 04:41 PM
C
Member
Join Date: May 2015
Location: USA
Posts: 3,138
Received 2 Votes on 2 Posts
Just take the hot line for the fan, run it to the common contact on both relays, and run the normally open contact on both relays to the fan. It won't hurt anything if both relays are on at the same time as long as both are controlling the same load.
 
  #3  
Old 12-15-16, 01:44 PM
T
Member
Join Date: Oct 2005
Location: USA
Posts: 1,650
Received 44 Votes on 43 Posts
Name:  Drawing1.jpg
Views: 1510
Size:  24.9 KB

the schematic of what carbide said.
 
  #4  
Old 12-15-16, 04:31 PM
E
Member
Thread Starter
Join Date: Dec 2016
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
Thanks,
Yes, that would work fine and I may just have to do something like this, but I'm trying to find a way to use the existing relay within the fan in a can instead. As you can see by the attached image of the can's wiring schematic, I'd like to be able to fire it's relay with either dryer's blower motor contactor's 24vac coil signal. I was going to wire them both in parallel to the fan's relay and that would work fine wither one was running indepently or both of the dryers were running at the same time. But then I realized by doing that if only one dryer was running I would be back feeding that 24v to the other dryers contactor coil, energizing it even if it was not called to run. I'm only concerned with the relay in the can, not the air pressure switch since I don't need to send a signal back to the dryer to start. Thanks again.
Name:  CAS-4 wiring.jpg
Views: 3776
Size:  20.8 KB
 
  #5  
Old 12-15-16, 06:05 PM
C
Member
Join Date: May 2015
Location: USA
Posts: 3,138
Received 2 Votes on 2 Posts
You need two relays to keep the dryers isolated from one another for the reason you state.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: