Is this the proper way to wire these circuits?
#1
Member
Thread Starter
Join Date: Dec 2007
Location: USA
Posts: 187
Received 0 Votes
on
0 Posts
Is this the proper way to wire these circuits?
I want to have two circuits for the lights in my pole barn. I drew this sketch to show how I plan on doing the wiring. I colored the hot wire red for clarity, but it will be black. I will be using #14 wire inside of 1/2" EMT. Is this the correct way to wire this? I hope its easy to see.Thanks. John.

Last edited by PJmax; 12-20-16 at 05:41 PM. Reason: added updated pic
#2
I don't see a problem with the wiring. How long are the runs? You have only two lights, or will you be tapping off the two for additional? Remember you can only have a 15 amp breaker for each circuit with the 14 gauge wire, which I am assuming will be THWN/THHN...
Depending on which code cycle your location uses, you may be required to run a neutral to the switch location and cap it off. Check first.
Depending on which code cycle your location uses, you may be required to run a neutral to the switch location and cap it off. Check first.
#6
You probably already know this, but if the picture is a junction box - you could combine the two conduits from the panel to the junction box. One 1/2" conduit can take 2 hots, 2 neutrals, and one ground.
Regardless, all grounds get connected in each box. (no desire to keep grounds separated like neutrals).
-Mike
Regardless, all grounds get connected in each box. (no desire to keep grounds separated like neutrals).
-Mike
#9
Maximum conduit fill for 1/2" EMT is 9 #12 conductors. You mentioned you are using #14 but I suggest you keep the maximum wire count to 9 because derating issues start if there is more then 9 wires.