disconnect detached garage
Old 12-21-16, 08:55 PM
A
Considering replacing an actual fuse box subpanel that is located in a detached garage. It is supplied by a 10/3 wire and protected by a 30 amp breaker inside the house where it is connected to another subpanel located next to the main panel. Garage does not have any type of machinery so it is only supplying lights, receptacles and garage door opener do not want to replace 10/3 wire.
To replace the fuse box looking at a square d 2space 4circuit subpanel qo or homeline model 24l70fs. After reading many threads here and elsewhere a disconnect is not needed in a subpanel if there are less than 6 breakers? Also, one ground rod is necessary but two are usually put in at the detached structure if multiwire circuits? Thanks for your help.
Old 12-21-16, 09:49 PM
ray2047's Avatar
Received 15 Votes on 13 Posts
Every thing sounds up to code if the 10-3 has a ground wire. If it doesn't it may be grandfathered but that will also change how the new panel will be setup.
Old 12-22-16, 04:50 AM
A
Yes it has a ground, 2 hots and a neutral.
Old 12-22-16, 05:55 AM
P
Received 210 Votes on 178 Posts
Sounds like you're good to go. The need of two ground rods is because NEC calls for one if the resistance to earth is 25ohms or less. To prove to an inspector you have 25ohms or less takes expensive testing so it's a lot cheaper to install an auxiliary rod.
Old 12-22-16, 06:38 AM
pcboss's Avatar
Received 148 Votes on 131 Posts
I would not limit myself to a 2/4 circuit panel.
Old 12-22-16, 06:48 AM
ray2047's Avatar
You will need to buy and add a ground bar to your new panel. I agree with PCBoss a bigger panel is good future proofing. Look at the price of main breaker panel kits.They come with several branch circuit breakers and when you figure the cost of the free breakers not that expensive.
Just to verify the cable to the garage is UF isn't it?
Old 12-22-16, 05:35 PM
A
UF cable is there. Yes will get ground bar. None of the panels would accept 10 gauge wire, not sure if there was a way to make it work but for now the 4 circuits are adequate. Thanks to all for the advice.
Old 12-22-16, 05:37 PM
ray2047's Avatar
None of the panels would accept 10 gauge wire.
Not a problem. You just pigtail a larger gauge wire to the #10.