Ground wire to metal box

I am using metal handy boxes for receptacles. 3232TRWR Pass & Seymour receptacles and metal covers. Do I need a separate ground wire for the box or will it be grounded with the receptacle?
 
  #2  
Old 12-22-16, 04:36 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,965
Received 6 Votes on 6 Posts
Not a separate grounding wire, just use a green grounding screw in the back of the box and loop your grounding wire around it before going to the receptacle. Self grounding receptacles are fine, but don't take into consideration someone later changing the receptacle to a non-grounding one.
 
  #3  
Old 12-22-16, 05:51 PM
B
Member
Thread Starter
Join Date: Jan 2011
Location: Hennepin County, MN, USA
Posts: 131
Received 0 Votes on 0 Posts
Is this receptacle self grounding? I don't want to use a screw to the box.
 
  #4  
Old 12-22-16, 06:44 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
I don't want to use a screw to the box
Why not. If it is an interference issue then use a grounding clip.
Is this receptacle self grounding?
The purpose of the self grounding receptacle is to not have to put a ground wire on the receptacle. It is not to use the receptacle to ground the box. If you use the receptacle to ground the box then you loose grounding if the receptacle is removed. You are creating a safety issue. The ground wire must go to the box if it is metal. There is no exception.
 
  #5  
Old 12-22-16, 07:31 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,799
Received 252 Votes on 220 Posts
3232TRWR are tamper resistant and weather resistant devices, they are not self grounding. For self grounding you need 3232TRSI for tamper resistant self grounding, or 3232SI for standard self grounding. I am not sure why you are using weather resistant devices.

I would also recommend not using handy boxed. The get overfilled too easy. I recommend using 4"x4" steel boxed with mud rings.
 
  #6  
Old 12-22-16, 08:56 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,222
Received 103 Votes on 89 Posts
Do not use handy boxes. They are too small for more than one cable and device. Use 1900 boxes with covers.
 
  #7  
Old 12-22-16, 11:21 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,541
Received 0 Votes on 0 Posts
You MUST ground the box. You do not need to ground the device if it's self grounding, or it's in a surface mounted box with the plastic washers removed.
 
  #8  
Old 12-23-16, 07:57 AM
B
Member
Thread Starter
Join Date: Jan 2011
Location: Hennepin County, MN, USA
Posts: 131
Received 0 Votes on 0 Posts
Thank you for the advice.
 
  #9  
Old 12-23-16, 03:04 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,799
Received 252 Votes on 220 Posts
One small note: The "I" in 3232SI indicates the color of the device. I = Ivory, W = White, LA= Light Almond. So a white standard self grounding receptacle would be 3232SW.
 
 