GFCI Test Problem

Separated from: http://www.doityourself.com/forum/el...gfci-test.html

How was this situation resolved? Was it the outlet? I'm facing a simular situation, GFCI and downstream outlets all test as good until I press the test button. Press the Test button, GFCI trips, test GFCI outlet, no lights, as it should be but all downstream outlet go to hot/grd reversed. Brand new outlet, also triple checked that feed and load sides are wired correctly.
 
Sponsored Links
  #2  
Old 12-29-16, 05:29 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,170
Received 1,116 Votes on 1,036 Posts
Welcome to the forums.

also triple checked that feed and load sides are wired correctly.
They are not !

When a GFI trips..... it becomes dead....NO hot or neutral on face of device and NO hot or neutral out of the load connections.


It is very possible that a plug in tester could show a strange reading when the GFI tripped.
The only positive way of knowing is to use a test light, voltage tester or analog meter.
 
  #3  
Old 12-29-16, 05:42 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
Note a voltage tester does not mean a non contact tester. They can give false positives. A solenoid voltage tester would be fine.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: