Landscape lighting transformer keeps tripping circuit
Old 02-03-17, 04:05 PM
B
I have a toroidal 1200W multitap landscape transformer servicing 5 circuits of approximately fifty 3-5W LED fixtures. It is on a dedicated circuit. I had a 20A AF-GFCI breaker that tripped fairly frequently when the circuit switches on. I replaced it with a regular breaker. It still trips, but less frequently.
It only trips when switching ON. Once on it stays on fine, and does not trip when switching OFF.
Not related to rain, moisture or weather.
The five circuits are all between 30-150ft 12G landscape wire. Probably much more copper than needed.
What could be causing this? Could there be an initial current surge beyond 20A.? If it is a "short" somewhere, why does it stay on, once it is on??
Thanks!
Old 02-03-17, 04:09 PM
Received 1,523 Votes on 1,406 Posts
A transformer has a primary winding and a secondary winding.
The power gets connected to the primary and the lights to the secondary.
There should not be any interaction between the primary and secondary which means nothing on the low voltage side can cause the GFI to trip.
There is a small chance that the transformer you are using has one leg of the secondary grounded. That would be something to look into. A make and model could help to clear up that point.
I see that a regular breaker is tripping too. That wouldn't be affected by a grounded secondary line. The total load on the transformer is roughly 250 watts ?
Old 02-03-17, 05:18 PM
B
That is correct.
I was wondering if all the copper in those parallel circuits could present such a low resistance initially, acting as a "sump" and draw too much current??? Wild guess......But then, these are designed for it.
Model is TR 1200-1222 (I think it represents 1200W from four 300W circuits) and 1222 represents the different taps from 12V-22V.
Thanks
Old 02-03-17, 06:58 PM
A
Received 134 Votes on 123 Posts
All that copper in those 12 gauge parallel circuits would not act as a sump and cause a brief high currnt draw. But you would need to keep all that copper to minimize voltage drop that could cause the lights at the far ends of the low voltage circuits circuits to be dimmer or to flicker.
You might want to get a clamp on ammeter to verify how much current you are really drawing.
Old 02-03-17, 07:05 PM
I recognize that transformer. I haven't sen that problem in the past.
I can understand an arc fault breaker tripping but not a standard 20A breaker.
I'm wondering if an HVACR circuit breaker would work without tripping.
I'm also wondering if this problem is related to the LED vs incandescent lamps.
I think I'd check with the manufacturer and see if they can shed any light on the problem.
Lightcraft outdoor/uploads/TR-1200-1222-SS.pdf
Old 02-21-17, 05:01 PM
B
I measured the current at the circuit breaker: 1.4Amp.
I have not spoken to the manufacturer yet
Old 02-21-17, 07:32 PM
The LED's can be like a dead short across the transformer until they illuminate.
You'd need a peak reading probe that locked the startup surge value.
I had checked to see if it says "incandescent only" and I didn't see it but the manufacturer may have different info that could be helpful.
Old 02-22-17, 07:19 AM
B
I spoke to manufacturer. This transformer is fine with LED's. It is an AC tranformer, and my lamps are AC and DC rated. He did not seem worried about number of LED's either.
His only suggestion was to place the entire load on just one or two of the transformer circuits, rather than spreading it over all four circuits.
I will update you!
Old 02-23-17, 09:48 AM
CasualJoe's Avatar
Received 111 Votes on 98 Posts
That would be a dual function AFCI/GFCI breaker, what code were you trying to meet? Are you in the Kansas City area?
boonjh
I think it's safe to say the breaker was not tripping on overload. You could have a bad dual function breaker.
I saw my first dual function AFCI/GFCI receptacle last week.
Old 02-23-17, 09:58 AM
B
No, This is happening with a regular 20A breaker.
(I was looking for a GFCI breaker to protect the outside receptacle....... I prefered it to using an outside GFCI outlet. The dual function breaker is much lower price. Figured having arc fault protection won't hurt??)
Old 02-23-17, 10:10 AM
CasualJoe's Avatar
A regular breaker will trip on overload or a direct short. If you correctly measured the current draw the breaker isn't overloaded.
Old 05-09-17, 02:14 PM
B
My working diagnosis is that the sudden current inflow to energize the transformer, causes the breaker to trip. (I have isolated the different load circuits on the transformer, without any luck)
My question is: could a "time delay breaker" fix the problem? (I have a panel that uses "SquareD" breakers)
Old 05-09-17, 08:23 PM
From Schneider Industries.....
QO-HM high-magnetic circuit breakers are recommended for area lighting (such as
athletic fields, parking lots, and outdoor signs), when using lamps of inherent high inrush current, individual dimmer applications or other applications where high inrush currents exceed standard tripping conditions. These circuit breakers are available in one-pole 15 and 20 A ratings only. QO-HM circuit breakers are physically interchangeable with standard QO circuit breakers and accommodate the complete range of QO accessories.
QO-HM circuit breakers are manufactured with the magnetic trip point calibrated at a
much higher level than standard QO circuit beakers.
That would be a QO120HM breaker. You may have to get it at an electrical supply house.
I'm not sure the home improvement stores carry them.
Square D (Schneider Electric) QO120HM High Magnetic HACR-Type 20A 120/240V Breaker
Old 05-13-17, 07:40 AM
B
Thanks PJMax
My electric panel only accepts the "homeline" squareD type breakers.
Do you perhaps know if there is such a breaker?
Old 05-13-17, 07:51 AM
B
I assume it is the HOM120HM