1 of 4 bathroom electrical down. All on same breaker.
Hi y'all.
Long time lurker. First time posting on the electrical forum.
So I've come across a strange one today. I have 3 bathrooms and one half bath all in one 20A circuit. Never had a problem till now. 1977 house. In one bathroom (that was a 2009 addition) all power is now out (bank of 4 led ceiling lights, vent fan and a gfci by the sink) are all without power. No other outlets in this bathroom. The other bathrooms are fine so it's not the 20A breaker. I read the sticky above. No odd gfci's in some other place that could have tripped. The gfci in the dead bathroom will not reset. No power to it. I don't recall if that gfci kills power to the overhead lights and fans or not. (Is that normal or abnormal to do that) I pulled the light and fan switch cover (it's a near new dimmer switch for the light bank, and a separate older switch for the vent fan) and checked for loose wires. All are secure on screws And/or wire nuts.
I have not pulled the GFCI to check it (not really sure what I'd be looking for other than obvious disconnected wires).
Only other bit of info I can think of that may be relevant is we have heard a mouse about the house in this area. Trying to catch it. Perhaps he chewed through some wires? Can a mouse chew through solid copper?
What steps should I follow now to logically troubleshoot this. I do have a multimeter and basic electrician tools.
Long time lurker. First time posting on the electrical forum.
So I've come across a strange one today. I have 3 bathrooms and one half bath all in one 20A circuit. Never had a problem till now. 1977 house. In one bathroom (that was a 2009 addition) all power is now out (bank of 4 led ceiling lights, vent fan and a gfci by the sink) are all without power. No other outlets in this bathroom. The other bathrooms are fine so it's not the 20A breaker. I read the sticky above. No odd gfci's in some other place that could have tripped. The gfci in the dead bathroom will not reset. No power to it. I don't recall if that gfci kills power to the overhead lights and fans or not. (Is that normal or abnormal to do that) I pulled the light and fan switch cover (it's a near new dimmer switch for the light bank, and a separate older switch for the vent fan) and checked for loose wires. All are secure on screws And/or wire nuts.
I have not pulled the GFCI to check it (not really sure what I'd be looking for other than obvious disconnected wires).
Only other bit of info I can think of that may be relevant is we have heard a mouse about the house in this area. Trying to catch it. Perhaps he chewed through some wires? Can a mouse chew through solid copper?
What steps should I follow now to logically troubleshoot this. I do have a multimeter and basic electrician tools.
#2
Group Moderator
Wow, 3 1/2 bathrooms all on one circuit!
In the bathroom with no power I would remove the cover plate from all the outlets and switches and check the wires to see if any incoming are hot. It may be as simple as a bad outlet or loose connection at the first box in the bathroom.
In the bathroom with no power I would remove the cover plate from all the outlets and switches and check the wires to see if any incoming are hot. It may be as simple as a bad outlet or loose connection at the first box in the bathroom.
#3
Welcome to the forums.
Pretty inconvenient to have that many rooms on a single GFI receptacle. If there is no power to the GFI it won't reset. Start there by checking for power on the line side of the receptacle.
Pretty inconvenient to have that many rooms on a single GFI receptacle. If there is no power to the GFI it won't reset. Start there by checking for power on the line side of the receptacle.
#4
Member
It's also possible the mouse chewed through the insulation on the wires creating a ground fault. The GFCI won't reset if there is a continuous ground fault. As mentioned above, first step is to find out if there is power to the GFCI. If there is, then disconnect the load side of GFCI and try resetting it. If it resets, you have a problem downstream. Maybe the mouse...maybe coincidence.
#5
Member
Thread Starter
Join Date: Feb 2017
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thank you for the responses so far!
Some further detail.
Every other bathroom on this breaker also has a GFCI by each sink. What I meant previously is there are no tripped gfci's anywhere in the house that I can find. None on this circuit for sure.
So I want to get this GFCI thing straight. It is normal and proper for bathrooms wired up IAW Electric Code to make everything in that room lose power when a GFCI trips (or fails)? If so, I gotta be honest, that just makes no sense to me. Why would you want your overhead lighting to go out in the event of a GFCI tripping at your sink? If this does end up being the culprit, (tomorrow I'm going to see if the input to this GFCI is hot, as suggested) would it indicate it was wired wrong and needs to be rewired?
Some further detail.
Every other bathroom on this breaker also has a GFCI by each sink. What I meant previously is there are no tripped gfci's anywhere in the house that I can find. None on this circuit for sure.
So I want to get this GFCI thing straight. It is normal and proper for bathrooms wired up IAW Electric Code to make everything in that room lose power when a GFCI trips (or fails)? If so, I gotta be honest, that just makes no sense to me. Why would you want your overhead lighting to go out in the event of a GFCI tripping at your sink? If this does end up being the culprit, (tomorrow I'm going to see if the input to this GFCI is hot, as suggested) would it indicate it was wired wrong and needs to be rewired?
#6
bathrooms wired up IAW Electric Code
all power is now out (bank of 4 led ceiling lights, vent fan
You have a mess I'd actually consider straightening out the mess and then see if there was still a problem.
#7
Member
Thread Starter
Join Date: Feb 2017
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
So based on what I'm understanding here, unless wired wrong, a failed gfci is not likely to cause the lights and vent fan above it to also go out.
So what is the most likely failure here that could cause all these things (gfci, lights, fan) to go out in this bathroom but nothing else in the other 3 bathrooms on the same circuit?
So what is the most likely failure here that could cause all these things (gfci, lights, fan) to go out in this bathroom but nothing else in the other 3 bathrooms on the same circuit?
#8
Member
Thread Starter
Join Date: Feb 2017
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
HOLD THE PHONE. I figured it out. Or you guys did rather. Thank you!
I'm embarrassed to say that I didn't throughly check all the gfci's after all.
sure enough my upstairs 1977 bathroom had a towel hanging in such a way that it sort of hid that the button was tripped. Pushed it in and power came back on to the whole newer era downstairs bathroom.
So other than having 3 1/2 bathrooms on one 20A which I admit seems excessive, did the electrician wire this newer bathroom wrong by feeding the overhead lights and fan from this gfci? Is there a relatively easy way to have this fixed (separate lights and fan from gfci) without running a whole new line to the main breaker and/or Busting drywall?
I'm embarrassed to say that I didn't throughly check all the gfci's after all.
sure enough my upstairs 1977 bathroom had a towel hanging in such a way that it sort of hid that the button was tripped. Pushed it in and power came back on to the whole newer era downstairs bathroom.
So other than having 3 1/2 bathrooms on one 20A which I admit seems excessive, did the electrician wire this newer bathroom wrong by feeding the overhead lights and fan from this gfci? Is there a relatively easy way to have this fixed (separate lights and fan from gfci) without running a whole new line to the main breaker and/or Busting drywall?
#9
did the electrician wire this newer bathroom wrong by feeding the overhead lights and fan from this gfci?
Is there a relatively easy way to have this fixed (separate lights and fan from gfci)
#10
Member
I'm embarrassed to say that I didn't throughly check all the gfci's after all.
sure enough my upstairs 1977 bathroom had a towel hanging in such a way that it sort of hid that the button was tripped. Pushed it in and power came back on to the whole newer era downstairs bathroom.
sure enough my upstairs 1977 bathroom had a towel hanging in such a way that it sort of hid that the button was tripped. Pushed it in and power came back on to the whole newer era downstairs bathroom.
What I mean is you should not be using a GFCI down line from another one if the previous one is protecting "load" down line. Although there really is not a hazard in doing this it can cause "phantom" tripping where the GFCIs trip one another. If there is a GFCI in bathroom one (first bathroom on the circuit) and the"load" is protecting the other bathrooms then no need for GFCIs in the other bathrooms.
If you know the circuit layout then you can simply take the conductors out of the "load" sides of the GFCIs and place them on the "line" sides. This way only the GFCIs themselves are protected and one GFCI to a previous bathroom will not affect another bathroom down line in the circuit.