Bathroom fan humidity switch required Neutral wire
#1
Bathroom fan humidity switch required Neutral wire
BATHROOM 1
I have a bathroom that has two wall switches. One is for the light and the other is for the fan. I want to install a Leviton IPHS5-1LI Humidity Sensor, but when I looked behind the switch there are 2 black wires and ground. There is no neutral wire. How can I wire this humidity switch?
BATHROOM 2
I have a 2nd bathroom that I wanted to replace the ceiling light with a fan that comes with a light and change the single switch to double. That wall switch also has 2 black wires and no neutral. The house was built in 2001 and I would assume it would have a neutral wire. Thanks in advance for any help given.
I have a bathroom that has two wall switches. One is for the light and the other is for the fan. I want to install a Leviton IPHS5-1LI Humidity Sensor, but when I looked behind the switch there are 2 black wires and ground. There is no neutral wire. How can I wire this humidity switch?
BATHROOM 2
I have a 2nd bathroom that I wanted to replace the ceiling light with a fan that comes with a light and change the single switch to double. That wall switch also has 2 black wires and no neutral. The house was built in 2001 and I would assume it would have a neutral wire. Thanks in advance for any help given.
Last edited by PJmax; 03-08-17 at 03:11 PM. Reason: added graphics
#2
Is there a bundle of white wires in the back of the box? If so that is the neutral connection, as for the other bathroom it sounds like you will need another conductor from the switch to the fan if you intend to swith them separately,post a pic of the conductors in the box.
Geo
Geo
#3
I looked to the back and there were not white wires. I thought I took a picture of the inside, but I didn't. I'll check again tomorrow. Here are some pictures:





Last edited by PJmax; 03-08-17 at 03:06 PM. Reason: added graphics/enhanced pics
#5
Look all the way in the back of the box. You have two cables coming into the box (single gang) which will mean you will have a neutral. I think I can even see it in the picture.

#6
Assuming there is a white wire in that single bundle on both bath. If I buy the Humidity Sensor Switch, all I have to do is run a white wire from the switch and add it to the bundle? I think the switch requires a white wire connection directly to the switch.
https://www.youtube.com/watch?v=K58CptgPGGg
https://www.youtube.com/watch?v=K58CptgPGGg
#8
I added labeling to keep the two bathrooms separate.
Bathroom 1 has two switches. It looks like there should be a neutral/white bundle in there but the pictures don't allow us to see the back of the box.
Bathroom 2 definitely has a neutral/white bundle (as Tolyn pointed out) however you don't need a neutral at this box. You need two switchable hot lines to the light. If there is not a red wire in this box then you cannot use a dual switch here as you do not have two switched lines.
====================================================
You should also consider a countdown timer is place of a humidity switch. Although a humidity switch sounds like a great idea..... they can take too long to activate and keep the fan running longer than it needs to.
I install a 1 hour pushbutton countdown timer. Especially effective when the toilet is used for a number two.
Bathroom 1 has two switches. It looks like there should be a neutral/white bundle in there but the pictures don't allow us to see the back of the box.
Bathroom 2 definitely has a neutral/white bundle (as Tolyn pointed out) however you don't need a neutral at this box. You need two switchable hot lines to the light. If there is not a red wire in this box then you cannot use a dual switch here as you do not have two switched lines.
====================================================
You should also consider a countdown timer is place of a humidity switch. Although a humidity switch sounds like a great idea..... they can take too long to activate and keep the fan running longer than it needs to.
I install a 1 hour pushbutton countdown timer. Especially effective when the toilet is used for a number two.

#9
OK, I just doubled checked and both bathrooms have white (neutral) wires bundle in the back. So if I where to connect a humidity sensor to Bathroom 1, I would connect a separate white wire from the sensor switch and add it to the neutral bundle.
For Bathroom 2, to replace the light for a bath fan/light, I would remove the current light, install the bath fan with the current wiring used for the light. Then I would have one switch that would run the fan and the light at the same time, since there is no red wire to run a Dual switch. Correct?
If I wanted a dual switch I would need that red wire.
Thanks to everyone who took their time to help me out. I want to let you know, how much I really appreciate the help and suggestion gven. I know your time is valuable.
For Bathroom 2, to replace the light for a bath fan/light, I would remove the current light, install the bath fan with the current wiring used for the light. Then I would have one switch that would run the fan and the light at the same time, since there is no red wire to run a Dual switch. Correct?
If I wanted a dual switch I would need that red wire.
Thanks to everyone who took their time to help me out. I want to let you know, how much I really appreciate the help and suggestion gven. I know your time is valuable.
#10
Then I would have one switch that would run the fan and the light at the same time, since there is no red wire to run a Dual switch.
You'd have to replace a two wire cable with a three wire cable or add an additional two wire cable.