Meter socket (jaw) burnt off

I was having partial intermittent power loss to my single family dwelling. Power company said I needed to have an electrician replace the meter socket "jaws". He provided a temporary jump and disconnected the 240 service to my house. He didn't think it was a big job.

The first electrician said I needed to upgrade from a 100 amp service to 200 amp service at a cost of $3,500. I know upgrading would be a good idea but is this really necessary? I've attached photos - looks like the plastic behind the meter burnt somewhat but this could be from the connection arcing. You think the lug just separated or did I truly overload my service.

twelve years ago we re-did the kitchen and a second panel was added. never had a problem before or with breakers tripping. Our biggest draws would be an electric dryer, ac, and electric oven.

I'm trying to get a second opinion but everyone is busy. Any help would be appreciated

thanks TonyName:  pic1.jpg
Views: 1905
Size:  34.4 KBName:  pic2.jpg
Views: 1299
Size:  37.3 KB
 
Sponsored Links
  #2  
Old 03-07-17, 08:16 AM
Member
Join Date: Jun 2012
Location: USA
Posts: 1,416
Received 12 Votes on 11 Posts
If you have a 100 amp main panel / 100 amp main breaker then the maximum load should have only been 100 amp. If the case then you would not have overloaded the meter socket, just a loose connection. Get a few more quotes.

Did the electrician do a load calculation? Otherwise suggesting an upgrade is just a sales tool. Still most times with an electric oven, a/c, and dryer you get pushed over 100.
 
  #3  
Old 03-07-17, 08:20 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,941
Received 30 Votes on 26 Posts
Unless you are planning to add large loads I would just change the meter socket.
 
  #4  
Old 03-07-17, 08:28 AM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 5,451
Received 0 Votes on 0 Posts
I'm not an electrician but have run into this problem before. It was fairly easy to find the parts and replace them.
The power company will help you out by cutting and reconnecting the feed.
 
  #5  
Old 03-07-17, 09:14 AM
Member
Thread Starter
Join Date: Mar 2017
Posts: 5
Received 0 Votes on 0 Posts
Thanks for the quick responses. I thought upgrading was excessive. I could see if this happened during the summer when the Central AC is running. We are not nearly using as much power this time of year (really only electric dryer)
 
  #6  
Old 03-07-17, 09:47 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,062
Received 370 Votes on 347 Posts
It would be extremely rare to finds parts for that old meter pan.

That means the upper service cables will need to be pulled out so that the pipe can be unscrewed from the top of the meter pan so that the pan can be replaced. Depending on the condition of the wire in the pipe.... it may need to be replaced too.
 
  #7  
Old 03-07-17, 10:50 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: USA
Posts: 4,016
Received 17 Votes on 17 Posts
Is that meter fed by cable or is it piped?a new rectangular 100 amp socket will give you some wiggle room with the conductors however the load side maybe a bit of an issue , is it piped or cable?did the POCO have any suggestions on where you may find jaws?
Geo
 
  #8  
Old 03-07-17, 11:09 AM
Member
Thread Starter
Join Date: Mar 2017
Posts: 5
Received 0 Votes on 0 Posts
piped to the roof then overhead cable. The POCO recommended switching some of the load to the other side (not sure that is possible my two panels are pretty much full) - other than that they had no comment. Just got a price of $2,500 for new service, ground, panel. I'm thinking I might be better off spending the $2,500 for the upgraded service rather than $500 - $700 for a new socket. Any thoughts.
Name:  Capture.jpg
Views: 827
Size:  35.6 KB
 
  #9  
Old 03-07-17, 11:24 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: USA
Posts: 4,016
Received 17 Votes on 17 Posts
Not sure where you live but that sounds like a descent price,combining your 2 panels into one,make sure the leave extra spaces in the panel for future expansion.
Geo
 
  #10  
Old 03-07-17, 12:19 PM
Member
Thread Starter
Join Date: Mar 2017
Posts: 5
Received 0 Votes on 0 Posts
Massachusetts. below are my two existing panels
Name:  IMG_5829.jpg
Views: 897
Size:  32.5 KB
 
  #11  
Old 03-07-17, 01:25 PM
Member
Join Date: Jun 2012
Location: USA
Posts: 1,416
Received 12 Votes on 11 Posts
If you can afford it then go for it. You will sleep better knowing it is done.
 
  #12  
Old 03-07-17, 01:32 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,062
Received 370 Votes on 347 Posts
A lot of circuits there for a natural gas house. Both look like decent Sq D panels.
 
  #13  
Old 03-07-17, 04:57 PM
Member
Thread Starter
Join Date: Mar 2017
Posts: 5
Received 0 Votes on 0 Posts
yes two square d panels. After talking to three electricians I am going to upgrade (I have over 40 breakers). He did say he would have to use some mini breakers (and leave some empties) - which I've read is perfectly ok as long as the panel supports it. Piece of mind and for slightly more than double the price of replacing the socket I think I'm getting much more value.

The electrician uses Murray breakers - I'm going miss the Square D
 
  #14  
Old 03-07-17, 05:01 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,062
Received 370 Votes on 347 Posts
The electrician uses Murray breakers - I'm going miss the Square D
You're paying the bill...... request Square D QO.
 
  #15  
Old 03-07-17, 07:00 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,965
Received 59 Votes on 52 Posts
If they installed another Square D QO panel they could reuse the breakers.

If it was me I would only replace the smaller one on the right, which is your main service, and leave the one on the left as a sub panel. It still has 7 openings, from what I can see, and the new panel will also have spare openings too. It would be a win - win.
 
  #16  
Old 03-07-17, 07:06 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: USA
Posts: 4,016
Received 17 Votes on 17 Posts
I don't really like the idea of a new service with mini breakers,how about removing only the bigger existing panel,and installing a new 200 amp 40 cir. with main and feeding the smaller sub panel from it, I agree with PJ ,stick with the SQ D breakers you should be able to reuse them.
JMO
Geo
 
  #17  
Old 03-07-17, 09:57 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,941
Received 30 Votes on 26 Posts
I too would vote to reuse the Square D breakers. Going with other brands you lose the Visi-trip indicator window.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: