My new home - electrical questions
Hi everyone I bought a house last year and we have seen slowly fixing I think up. I have a 100amp service panel and next to it is a sub panel that powers the finished basement. The sub panel is being fed by a 60 amp breaker. In the garage I have a second sub panel that is being fed of the same 60amp for the basement. I have checked the wire size going to the basement and it's a12g so I know it kind of small. I will be running 8 or 6g depending on what I hear from you guys here. The panel in the garage has two breakers one 15amp and one 20amp. What I need is a 220v 30amp to run my welders. Would I be able to run the 220v off of the 60amp or would I need to run it off the 100amp that is in the main panel. The sub panel in the garage only has room for the two breakers it has now so I would need to buy a new panel. Would running off the 100amp be safer then running off the 60amp. I worry that the 60amp would be over loaded. I plan on in the future to have a 200amp service being put in I just can't afford to have a electrician come in and do that now
Thanks for the help in advance.
Paul Wong
Thanks for the help in advance.
Paul Wong
#2
The sub panel is being fed by a 60 amp breaker.... size going to the basement and it's a12g
What I need is a 220v 30amp to run my welders. Would I be able to run the 220v off of the 60amp or would I need to run it off the 100amp that is in the main panel.
#3
Welcome to the forums!
If the sub panel is fed with a 60 amp breaker in the main panel, the wire feeding it should be #6 copper. It should be fed with two hots, one neutral, and a grounding path. This could be a wire or a metallic raceway. If any of this is not correct this should be fixed first.
The feeder going to the garage could be fed off the sub panel, or the main panel. It should not be fed off the same breaker by connecting two wires (the sub panel feeder and the garage feeder) to the same lug on the 60 amp breaker. This is called double lugging and is not allowed. The way to do it properly is to install a separate breaker for the garage feeder (ideal) , or to splice the sub panel and garage wires together and then connect another short piece of wire to the breaker. (pigtail) You should NEVER connect any wires to the main feeders coming into the main panel.
The garage feeder wires needs to be sized to the size breaker protecting the wires. Again, if it is 60 amps it will need to be #6 copper. What you have in the garage now for a feed will determine if you you can do. If you only have 2 wires (hot and neutral) you can only have 120 volts or 240 volts, not both. You would need 120 volts to run lights and smaller power tools and 240 volts for your welders, so really you need 4 wires, hot, hot, neutral, ground.
I highly doubt you will need more power then 60 amps to either the basement, or garage, unless your house is quite large or have a lot of electric appliances. Let us know what you have in wiring, and we can go from there.
If the sub panel is fed with a 60 amp breaker in the main panel, the wire feeding it should be #6 copper. It should be fed with two hots, one neutral, and a grounding path. This could be a wire or a metallic raceway. If any of this is not correct this should be fixed first.
The feeder going to the garage could be fed off the sub panel, or the main panel. It should not be fed off the same breaker by connecting two wires (the sub panel feeder and the garage feeder) to the same lug on the 60 amp breaker. This is called double lugging and is not allowed. The way to do it properly is to install a separate breaker for the garage feeder (ideal) , or to splice the sub panel and garage wires together and then connect another short piece of wire to the breaker. (pigtail) You should NEVER connect any wires to the main feeders coming into the main panel.
The garage feeder wires needs to be sized to the size breaker protecting the wires. Again, if it is 60 amps it will need to be #6 copper. What you have in the garage now for a feed will determine if you you can do. If you only have 2 wires (hot and neutral) you can only have 120 volts or 240 volts, not both. You would need 120 volts to run lights and smaller power tools and 240 volts for your welders, so really you need 4 wires, hot, hot, neutral, ground.
I highly doubt you will need more power then 60 amps to either the basement, or garage, unless your house is quite large or have a lot of electric appliances. Let us know what you have in wiring, and we can go from there.
#4
Member
Thread Starter
Join Date: Mar 2017
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The 60amp runs the cooktop and stove. I have a gas furnace and a gas water heater. The 60amp that goes to the sub in the basement has a 6g wire then the wire is 12 going to the garage sub.
#6
Member
Thread Starter
Join Date: Mar 2017
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I have a black a red and a blue neutral going to the garage. When I run the new wires do I need 3 or 4 wires. The sub in the garage has a neutral and a ground. The ground goes to a copper grounding rod.
#7
I have a black a red and a blue neutral going to the garage.
When I run the new wires do I need 3 or 4 wires.