Wire gauge

Ok here is my situation I have 12/2 wire run to well pump which is 100' from panel box.The pump is a 115 amp pump not 220.
This is on a 30 amp breaker and these are the items I have running from this one breaker.Well pump, 2 - 5000 btu air cond. and ceiling fan,Sterio system all of this could be running at one time on some days.Do I need larger breaker and larger wire or is ok like it is.Thanks for your help
 
  #2  
Old 04-02-17, 09:05 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,773
Received 1,324 Votes on 1,224 Posts
You're running the well pump, 2 A/C's, a ceiling fan and a stereo all on one 12/2 cable on a 30A breaker ?

If that is correct.... you do need larger wire with the correct circuit breaker.
#12 wiring should only be connected to a 20A breaker.

I'm trying to understand what you are doing. Is the pump house a club house ?
 
  #3  
Old 04-02-17, 09:08 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
This is on a 30 amp breaker and these are the items I have running from this one breaker.Well pump, 2 - 5000 btu air cond. and ceiling fan,Sterio system all of this could be running at one time on some days.
The maximum breaker size for a 120 volt general purpose circuit is 20 amps. Your existing breaker is too large.

If the items are scattered throughout your house you need to run a dedicated circuit that is just for the pump and maybe a light.

If this is all at the pump house your best solution is to instal a minimum of a 40 amp subpanel connected to a 240v 40 amp breaker in your main panel. You will need either 8-3 UF cable direct buried or four #8 THWN wires (two back, one white, one green) in conduit. I'd suggest a 100 amp main breaker panel kit for the subpanel at the well.
 

Last edited by ray2047; 04-02-17 at 09:27 PM.
  #4  
Old 04-02-17, 11:31 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,218
Received 103 Votes on 89 Posts
You have several issues that need to be taken care of before a fire happens. Please review the above posts for direction.
 
  #5  
Old 04-03-17, 02:40 AM
W
Member
Thread Starter
Join Date: May 2015
Posts: 69
Received 0 Votes on 0 Posts
Disconect

THanks for all the help.I went ahead and put well pump on a 20 amp breaker and nothing else on this but well pump.The other items I had on this right now is not connected to any breaker. I will install another breaker for 2 air conditioner ceiling fan and lights.The 2 air conditioners are 115 volts .What size breaker do I need to use and also wire size.Thanks very much for your help.
 
  #6  
Old 04-03-17, 02:48 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
Ideally one 15 or 20 amp circuit for each A/C. Then split the lights and ceiling fan between the circuits. Assumes the A/Cs draw 7 amps or less (Usually a 5000 BTU will.) #14 for 15 amps and #12 for 20 amps. Since this is new wiring I suggest 20 amp for each circuit. That will give you a little future proofing. (A 5000 BTU doesn't cool very well and you may need larger ones.)
 
  #7  
Old 04-03-17, 04:03 AM
W
Member
Thread Starter
Join Date: May 2015
Posts: 69
Received 0 Votes on 0 Posts
Wire Guage

Thanks for all the advice.I really do appreciate the help.
 
  #8  
Old 04-03-17, 04:06 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
Let us know if you have any more questions.
 
 

Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: