Get two 120v circuits from one 240v circuit?

If you have a 240v 4 wire circuit (hot, hot, neutral, ground) and the 30 amp breaker it currently has was replaced with a 20 amp breaker, is there a code conforming way to "split" the hots at the outlet to provide two 120v 3 wire 20 amp circuits?

I'm thinking some sort of adapter must exist to do this, unless there's a safety reason why this would be a terrible idea that makes it against code.
 
Sponsored Links
  #2  
Old 04-15-17, 12:00 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 56,979
Received 825 Votes on 775 Posts
That is the basis behind a multi wire branch circuit.
You would remove the 30a breaker and install a 2P20A breaker like what would be used for a 240v circuit.

The neutral is shared between the two circuits. It can be as simple as a wire nutted splice.
In this type of circuit.... the neutral is very important so ensure that a good splice is made.

Just one wiring example.....
Name:  MWBCD.jpg
Views: 6135
Size:  18.2 KB
(grounds not shown for clarity but must be connected)
 
  #3  
Old 04-15-17, 01:08 PM
S
Member
Thread Starter
Join Date: Feb 2014
Posts: 9
Received 0 Votes on 0 Posts
I was asking terms of whether it would be possible to get the 30A breaker replaced with 20A, but leave the existing 240v twist lock receptacle in place (I think it is L14-30) Then use some sort of adapter that would have a L14-30 male plug on one end, and provide two standard 5-15 or 5-20 120v female plugs on the other for ordinary 120v stuff to plug into. The adapter would basically be wired the same as your diagram.

Due to subsequent remodeling where the receptacle is located it would be very difficult to get at it to change, let alone add a second one. It is hard enough to access to plug/unplug stuff into it! I was hoping there might be a way where the only electrical work was replacing the circuit breaker, and there was an adapter I could buy rather than huge difficulty (and big $$$ I'm sure) of having the receptacles changed as in your diagram.
 
  #4  
Old 04-15-17, 01:25 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,113
Received 69 Votes on 59 Posts
Receptacles are made to avoid someone plugging in to an incorrect voltage or ampacity. The devices should be changed.
 
  #5  
Old 04-15-17, 01:41 PM
S
Member
Thread Starter
Join Date: Feb 2014
Posts: 9
Received 0 Votes on 0 Posts
If such an adapter split the two hot legs between the two 5-15 female plugs (i.e. one to each) and sharing the ground and neutral, how would it be possible to plug in the incorrect voltage or ampacity? You'd have 120v 15A plugs, each effectively on its own circuit, same as if you rewired it as in PJmax's drawing.
 
  #6  
Old 04-15-17, 02:56 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,138
Received 55 Votes on 48 Posts
Are you talking generator here???

 
  #7  
Old 04-15-17, 03:21 PM
S
Member
Thread Starter
Join Date: Feb 2014
Posts: 9
Received 0 Votes on 0 Posts
I wasn't talking generator, but that appears to be exactly what I was after! Checking a few places that sell a similar looking generator adapter, it is indeed able to take a generator's 240v L14-30 output and split it between to separate 5-20 circuits, each getting one of the 240v circuit's hots. So it would work on a 240v household circuit in the same way (I will still have the 30A breaker replaced with 20A for safety, even though I'm pretty sure I'd never exceed even 15A on either with what I want to plug in)

I figured something like this had to exist, but I didn't know what to ask google for. Thanks!!
 
  #8  
Old 04-15-17, 04:37 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,138
Received 55 Votes on 48 Posts
IMO if your running cord from that outlet change the breaker to GFI or make/buy and cord with GFI's in it..

[ATTACH=CONFIG]79618[/ATTACH]
 
Attached Images  
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: