Selecting the right breaker size
Received 0 Votes
Hi,
I need some feedback on what size of breaker I need. The conductor size is 10mm2 with 4 copper cores 6 strands each. Application is 220V 3 phase AC with Neutral.
According to the wire specifications, the maximum load for a 4 core 10mm2 cable when enclosed in the wall within a conduit is 46A at 30C (86F) ambient, conductor operating temperature being 70C (158F).
The circuit breaker I selected was a 4 pole 40A breaker, which I thought would be sufficient and would give me a 6A buffer.
But I had not compensated for high ambient temperature. So I re-did the calculations to compensate for high ambient temperature. The wire rating factor is 0.82 at a temperature of 40C (104F). This is the maximum ambient temperature that I am forecasting. So the maximum current the wire can carry is now recalculated as 46 x 0.82 = 37.72A.
So my question is should I go for a 30/35A breaker instead of 40A? Please note that I will never be pulling 46A through the wire. The wire will be under continuous load, the maximum continuous current being 35A. Should I stick to the 40A breaker or should I select a 30/35A one. I am also concerned about the wire temperature. I wouldn't mind decreasing the load a bit to keep the wire a bit cooler.
Would appreciate your opinion on this. Thanks.
Our electrical codes are not the same as those in Pakistan.
It sounds like you are stuck using a 40A breaker at this time without increasing wire size.
Received 0 Votes
I don't have the option of increasing wire size because the wiring is already done but I do have the option of reducing the load. The wire is going to be connected to a 3 phase solar inverter, so I can divide the load among three phases.
For a continuous maximum load of 35A would I not be ok with a 30A breaker or do I need to go lower?
Received 0 Votes
From what I gather, if the maximum load the conductor can handle is 37A, then to be on the safe side, the breaker I should use is 30A and my maximum continuous load should be less than 30A.
Would that be ok?
Would that be ok?