Mini Split Hvac - Disconnect

I know a disconnect must be within ~sight~ for code, but what is the rules/guidelines. The most common being a disconnect literally within hands reach if standing if front of the condensor.

Just thinking, mulling...
If I had a outdoor NEMA rated load center, acting as subpanel - could I not just tie all my minisplits-disconnects into this one single box Roughly anywhere from 5-7 feet away from all the minisplits ?
 
  #2  
Old 04-28-17, 04:55 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 36 Votes on 28 Posts
Yes, you can. The requirement is no more than fifty feet and in a direct line of sight.
 
 