Problem getting 120v circuit off 240v hot tub sub panel

I am not an electrician but have pretty extensive experience with DIY projects including some electrical. I'm stuck:

I want to run a 120v circuit off my hot tub sub panel to run some string lights.

Name:  Photo May 14, 4 13 13 PM.jpg
Views: 4523
Size:  44.7 KB

In the picture attached, the circuit I am adding is coming in from the bottom left: black, green, white. I put the white to the common bar, green to ground, and with the black (in the pic it is not attached and just has a wire nut on it), I pigtailed it to the red leg of the 20A two-pole breaker. Outside the sub panel, I first installed a 20A GFCI outlet and as soon as I power the sub panel from the 50A breaker at the main, the 20A two-pole breaker in the sub panel trips. The second thing I tried is to replace the 20A GFCI outlet with a standard 20A outlet and the interesting thing is that it did not trip the breaker at first, but only when I plugged something into the outlet.

Any help is appreciated. Thanks. (sorry picture is rotated - can't figure out how to fix that)
 

Last edited by ray2047; 05-16-17 at 09:51 AM. Reason: Rotate image.
  #2  
Old 05-16-17, 12:04 PM
R
Member
Thread Starter
Join Date: May 2017
Location: United States
Posts: 6
Received 0 Votes on 0 Posts
Yes, there is 240 between red and black coming in. Also the panel has been working fine and running the hot tub for about 3 months now.
 
  #3  
Old 05-16-17, 12:35 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,581
Received 13 Votes on 11 Posts
Also the panel has been working fine and running the hot tub for about 3 months now
Is it a 120 volt hot tub?
 
  #4  
Old 05-16-17, 12:46 PM
R
Member
Thread Starter
Join Date: May 2017
Location: United States
Posts: 6
Received 0 Votes on 0 Posts
No, the tub is all 240. I'm not sure why there are two separate 240 breakers feeding the tub but that's how it was installed by an electrician. The tub is fancy and has multiple jet speeds, lights, etc.
 
  #5  
Old 05-16-17, 12:50 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 62,083
Received 1,509 Votes on 1,396 Posts
Technically since that panel only has room for 2) two pole breakers and they are both feeding the hot tub.... you can't tie a 120v circuit in.
 
  #6  
Old 05-16-17, 02:12 PM
R
Member
Thread Starter
Join Date: May 2017
Location: United States
Posts: 6
Received 0 Votes on 0 Posts
Yeah, Pjmax, I am aware I was cheating a little and that it would not meet code. I'm not too worried about that. Thanks.
 
  #7  
Old 05-16-17, 03:48 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 62,083
Received 1,509 Votes on 1,396 Posts
Those both look like GFI breakers. That means you can't tap a 120v load from either one as that will unbalance the circuit and trip the GFI.

On a 2 pole GFI breaker.... you have to draw an even load across both legs. A 240v load by its nature does that.
 
  #8  
Old 05-16-17, 04:08 PM
R
Member
Thread Starter
Join Date: May 2017
Location: United States
Posts: 6
Received 0 Votes on 0 Posts
Bummer. I guess that means upgrading the sub panel. Well, thanks for the advice!
 
  #9  
Old 05-16-17, 06:40 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,480
Received 134 Votes on 123 Posts
Does the power in cable have a common (neutral) white conductor?

Without that you will need to string a new cable with red, black, white, and ground to the new subpanel.
 
  #10  
Old 05-16-17, 08:59 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 62,083
Received 1,509 Votes on 1,396 Posts
The breakers are the expensive part so find a panel where you can reuse those breakers.

Yes... there is a neutral there. A black wire taped white. :NO NO NO:
Either that wasn't inspected or the inspector missed the black wire taped white.
By code that wire is supposed to be white as any THWN smaller than #4 cannot be remarked.

Name:  gb.jpg
Views: 762
Size:  21.8 KB
 
  #11  
Old 05-17-17, 02:56 PM
T
Member
Join Date: Nov 2007
Posts: 391
Received 0 Votes on 0 Posts
On a 2 pole GFI breaker.... you have to draw an even load across both legs.
No you don't. 120/240 appliances never draw evenly because the 120v part is only connected to one leg.. It's tripping because the neutral is connected to the neutral busbar instead of the neutral (center) screw on the breaker. The breaker needs to be able to meter flow through the neutral in order to detect an imbalance.

I'm not sure why there are two separate 240 breakers feeding the tub
The 30A is for the heater, and the 20A is for the jet pump.
 
  #12  
Old 05-17-17, 03:50 PM
R
Member
Thread Starter
Join Date: May 2017
Location: United States
Posts: 6
Received 0 Votes on 0 Posts
taz420 wins. My son-in-law was at my house working on it this morning and that's exactly what he figured out. He connected the neutral to the center screw on the breaker and it works fine now.

Thanks all for your comments and advice.
 
 