Feeder line sizes

So from my meter/main-breaker (which comes in at a detached garage) I need to run 140 feet underground in conduit to get to the sub-panel at my house.

I'm planning to use aluminum (I'm poor, OK? ) and it's a 200 amp, single phase service.

My primitive calculations say #4/0 for both hots, #2/0 for neutral, and #6 for the ground.

Does that spec out? Or do I need to go fatter?
 
Sponsored Links
  #2  
Old 06-29-17, 01:16 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,666
Received 519 Votes on 489 Posts
Based on the distance..... you should experience acceptable sag up to 150A.

The 4/0 AL is rated for 205A.
2/0 AL for neutral is correct.
#4 AL for 200A service ground.

3" conduit would be a good choice.
 
  #3  
Old 06-29-17, 10:48 AM
Member
Thread Starter
Join Date: Apr 2013
Location: USA
Posts: 33
Received 0 Votes on 0 Posts
"....acceptable sag up to 150A."

Is that something you would be OK with? The house includes a small rental unit with its own appliances. Most of the appliances in both the main house and the rental run on gas (dryers, stoves, etc) so it seems like the chances of ever hitting above that 150 mark would be remote. But it is technically two households running on those feeders.
 
  #4  
Old 06-29-17, 11:28 AM
Member
Join Date: Jun 2017
Posts: 41
Received 0 Votes on 0 Posts
What is the sub panel for, are you remodeling or something? Depending on what all this is for you might not need as much as you think when it comes to amps. You have many options and they can mean big differences when it comes down to time money and headache. Also it's kind of odd having a main service at a garage then back feeding the house. It's legal but kind of uncommon so are these buildings existing or new.
 
  #5  
Old 06-29-17, 11:36 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,666
Received 519 Votes on 489 Posts
Gas is a plus and keeps the high electric demands down.

For that application the 4/0's should be ok.
 
  #6  
Old 06-29-17, 12:06 PM
Member
Thread Starter
Join Date: Apr 2013
Location: USA
Posts: 33
Received 0 Votes on 0 Posts
All the buildings are existing. The power drop has always come in at the detached garage, I assume because it's the closest building on the property to where the distribution lines run (we're pretty rural). The feeder lines from our side of the meter/main disconnect at the garage then run up to a separate mast, and then overhead (and through some trees) to the house. It's always been a bit hokey. Needless to say, getting those feeder lines underground has many advantages.
 
  #7  
Old 06-29-17, 02:52 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,666
Received 519 Votes on 489 Posts
If you already have power run overhead and it's working ok.... what size is that wire ?
If you're running larger then there should be no issues at all.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: