One exterior outlet dead...help.
Received 0 Votes
Howdy,
Looking for some help around an odd issue. I'm familiar (dangerous) with home electrical systems having done a lot of work around the house. Recently I was using an exterior outlet with a shop vac. It worked fine, no issues. After that I plugged in a line of exterior lights and the outlet was completely dead.
1. I've checked ALL GFCIs in and outside the house....testing each one. None were tripped.
2. I know specifically which GFCI this particular outlet is on and made sure it was working.
3. I've checked all breakers...none were tripped but I reset some just in case.
4. ALL the other outlets in the house work.
5. I swapped outlets with a new one that I tested inside and this also fails.
Seems to me it's a problem with the wiring to this specific outlet?
Any help is appreciated. House was built in 2004.
Thanks!
Thanks!
Welcome to the forums!
If you changed the receptacle (outlet) and it still doesn't work, the issue is likely in another box. If you check with a meter (not a non-contact tester) you should get 120 volts between black and white , and black and ground. You should also be able to read continuity between white and ground. If none of those tests work you will need to start going back on the circuit.
If you know which GFCI protects this outlet, that would be the next place I would go. Check to see if the LOAD side of the GFCI is putting out 120 volts between black and white. You can also test that the GFCI is working properly by going from LOAD black to ground. The GFCI should trip.
Received 0 Votes
Thanks guys. I did forget to mention that I tested white/black and it shows 13V.
The other exterior outlets are also on the same GFCI and they work.
I will go and test GFCI and see if that helps.
If you have 120 volts on the output then there may be another outlet between the GFCI box and the non working box. You need to start taking things apart until you find the fault.
I will also mention we have, many times in the past, had people tell us they have looked all over for the GFCI only to find one buried behind stuff in a garage or basement. Also, depending on the age of the house the GFCI could be in a bathroom, basement or garage.
Yes you need to open the others. Move any wires in regular recptacles that are in the back quick connects to the screws. (GFCIs don't have back stabs through the back wire connections look similar. However back wire connection are held by screw pressure so ate okay.)
so you have probably lost the hot.
You only have one GFCI in the circuit don't you?
Ground to black is also 13v