Tankless Water Heater Panel Connection
I'm installing a tankless water heater that requires one 60 amp breaker and #6 wire to serve it. I have installed breakers and new circuits in panels before but this panel is inset into the wall of the garage which presents an issue. Here's some info and my plan:
- Run individual #6 conductors (& ground) in PVC conduit from the heater to the panel along the surface of the garage wall (about 12 feet).
- The water heater has a 3-foot pigtail coming out of it with 2 #6 wires and one #8 ground.
- I plan to have a junction box to connect my new #6 wires to this pigtail, then run the new wires in conduit the 12 feet over to the panel.
- (for code purposes, I'm in Jacksonville, FL)
- (panel is a Siemens with 150 amp service)
- (I'm removing the old 30 amp breaker that served the old tank-style water heater)
- (a local electrician told me that my panel could definitely handle the new 60 amp breaker provided I took the old 30 out of service)
My question is, well.. first, does this sound ok so far, and then how do I route the three individual #6 wires the last 5 or 6 inches from the surface conduit run into the wall (through the drywall) so I can enter the panel though a knockout? I'm not sure there's enough room for a 90 degree sweep elbow to make that turn. Or can I just use a small 90 inside the wall from a junction box next to the panel (the box would provide a point for the surface conduit run to terminate).
Thanks.
Eric
- Run individual #6 conductors (& ground) in PVC conduit from the heater to the panel along the surface of the garage wall (about 12 feet).
- The water heater has a 3-foot pigtail coming out of it with 2 #6 wires and one #8 ground.
- I plan to have a junction box to connect my new #6 wires to this pigtail, then run the new wires in conduit the 12 feet over to the panel.
- (for code purposes, I'm in Jacksonville, FL)
- (panel is a Siemens with 150 amp service)
- (I'm removing the old 30 amp breaker that served the old tank-style water heater)
- (a local electrician told me that my panel could definitely handle the new 60 amp breaker provided I took the old 30 out of service)
My question is, well.. first, does this sound ok so far, and then how do I route the three individual #6 wires the last 5 or 6 inches from the surface conduit run into the wall (through the drywall) so I can enter the panel though a knockout? I'm not sure there's enough room for a 90 degree sweep elbow to make that turn. Or can I just use a small 90 inside the wall from a junction box next to the panel (the box would provide a point for the surface conduit run to terminate).
Thanks.
Eric
#3
You plan sounds fine. The only change you need to make is if the tankless is direct wired you need to have a disconnect instead of a junction box. An easy/cheap disconnect would be a 60 amp A/C non-fused disconnect. They run about $8.
#6
I was under the impression the water heater was in another room.
#7
Member
Thread Starter
Join Date: Jul 2017
Location: United States
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It is is the same room within sight of the panel (no conduit through doorways - haha). My main concern was how to make the connection to the panel from where I punch through the drywall at the end of the conduit (j-box). I didn't want to just have my 3 individual wires in the wall even for just 5 or 6 inches. So, I will run the conduit from the water heater over to just beside the panel, put in a junction box, then do 1 of 2 things:
1. Wire nut the #6 wires to 6/2 Romex and run it into the panel behind the drywall.
2. Use a short 90 degree elbow connecting the back of the j-box to the panel knockout for that last 6 inches behind the drywall.
1. Wire nut the #6 wires to 6/2 Romex and run it into the panel behind the drywall.
2. Use a short 90 degree elbow connecting the back of the j-box to the panel knockout for that last 6 inches behind the drywall.
#9
I didn't want to just have my 3 individual wires in the wall even for just 5 or 6 inches
Use a short 90 degree elbow connecting the back of the j-box
Option #1 is how I would likely do it.
#11
I would agree,remove some of the drywall and bring the pipe directly into the panel,no need to make any more splices.