Installing whole home surge suppressor

I am about to install a whole home surge suppressor. The version I have requires a dedicated 50amp breaker.
The recommendations I have read indicate the the surge suppression should be mounted high in the electrical panel (closer to main breaker) and the leads to the surge supressor should be a short as possible.

My electrical panel is mounted between 2x6 studs. so I can't easy mount the surge suppressor on the side (I suppose I could drill a hole in the 2x6 to one of the knockouts on the side of the panel)

If I install on the bottom of the panel (easy), the highest position the leads will reach are the 3rd and 4th breaker positions.

Is the effort to come in from the side and get closer to the main breaker worth it?

Appreciate anyone's comments.
 
Sponsored Links
  #2  
Old 07-24-17, 08:04 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,314
Received 45 Votes on 38 Posts
Can it be surface mounted above the panel and use a short piece of flex to get the breaker located at the top.

Name:  images.jpg
Views: 97
Size:  9.9 KB
 

Last edited by ray2047; 07-24-17 at 09:03 AM. Reason: Enlarge image.
  #3  
Old 07-24-17, 11:54 AM
I
Member
Thread Starter
Join Date: Nov 2008
Location: United States
Posts: 174
Received 0 Votes on 0 Posts
Thank you for the comment.
I don't have any knockouts available on the top of the box as all of the home circuits go through the top of the box. I will look tonight to see if some can be shifted to make room.

I wonder big is penalty on the surge suppression performance if I am down lower in panel?
Ian
 
  #4  
Old 07-24-17, 12:46 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
It can be mounted in the bottom of the panel if that is more convenient. The position of the breaker in the panel is rather irrelevant. The most important part is to have a quality earth ground, as short and straight path as practical.
 
  #5  
Old 08-04-17, 06:48 PM
I
Member
Thread Starter
Join Date: Nov 2008
Location: United States
Posts: 174
Received 0 Votes on 0 Posts
I ended up coming in from the side through the 2x6 using correct size hole saw. Worked like a champ.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: