100 amp service from 200 amp for Tiny home

Reply

  #1  
Old 08-03-17, 12:19 PM
G
Member
Thread Starter
Join Date: Aug 2017
Posts: 3
Received 0 Votes on 0 Posts
100 amp service from 200 amp for Tiny home

Hi, im new here and I wanted to get some opinions on running about 70-80 feet of service wire from my homes 200 amp service breaker panel to a 100 amp service for a new tiny home project. I would need all the things a home needs like hot water heater, split heating and air unit, stove, washer and dryer. I've been told numerous types of wire but i wanted to see if the 2-2-2-4 SER aluminum service wire would work? Thanks in advance and hope you're all having a great day!
 
Sponsored Links
  #2  
Old 08-03-17, 01:40 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
SER can not be buried even in conduit. Better and probably cheaper is to use mobile home cable. Note using #2 your supplying breaker is limited to 90 amps but the breaker in the subpanel can be greater because it is only used as a disconnect switch.
338.12 Uses Not Permitted.
(A) Service-Entrance Cable. Service-entrance cable (SE) shall not be used under the following conditions or in the following locations:
(1) Where subject to physical damage unless protected in accordance with 230.50(A)
(2) Underground with or without a raceway
(3) For exterior branch circuits and feeder wiring unless the installation complies with the provisions of Part I of Article 225 and is supported in accordance with 334.30 or is used as messenger-supported wiring as permitted in Part II of Article 396
 
  #3  
Old 08-04-17, 07:39 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
The wire you need depends on whether the local authorities consider this a separate dwelling unit. As Ray said if you use #2 aluminum it is only good for 90A. Dwelling units require minimum of 100A so you would need to increase the size of the cable. Is the construction permitted as a dwelling or is it more portable like an RV?

Are either of the panels located inside the buildings?

You'll also need to do a demand load calculation on your house's service to determine if it has sufficient capacity to support the second home.
 
  #4  
Old 08-04-17, 11:10 AM
G
Member
Thread Starter
Join Date: Aug 2017
Posts: 3
Received 0 Votes on 0 Posts
Thanks so much for your reply and help ray2047!!
 
  #5  
Old 08-04-17, 11:15 AM
G
Member
Thread Starter
Join Date: Aug 2017
Posts: 3
Received 0 Votes on 0 Posts
Hi and thanks so much for your reply ibpooks! Both panels are inside the homes. The tiny home we are working on is a 12x40 lofted barn cabin. It can be moved but doesn't have wheels or anything where you can just go with it without major work to move it so I consider it a dwelling. If i may ask how do i do the load calculation of my current home? Thanks again!
 
  #6  
Old 08-04-17, 08:51 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Just Google electrical load calculator.

Example: http://www.nojolt.com/load_calculations.shtml
 

Last edited by ray2047; 08-04-17 at 10:06 PM.
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: