Extending circuits
Extending circuits
Hello and happy Friday.
I need to extend some circuits about 3' to go into a sub panel. Three are BX with the bonding wire and five are Romex.
What is the best way to do this?
Can I use a large box or should I use several smaller ones?
Can the box(s) and all of the grounds be connected together and grounded by one larger wire?
Thanks in advance for the help.
Jim
Jim
You can use one box. It must be metal because of the Bx.
All neutrals must be combined. You only need one ground wire for all. Its size is based on the highest amp circuit. Metal boxes must be connected to the ground wire. Neutrals can not be combined.
Hi Ray,
Thanks for the quick reply.
I assume you meant all grounds must be combined in the first sentence.
Based on #14 and #12 wires can you recomend a box size?
Can a ground bar be used in the box to attach all of the grounds and a #12 wire run from it to the sub?
You will need to do a box fill calculation.
https://www.constructionmonkey.com/c...trical/boxfill
Yes.
can solid wire from Romex be used for the hots and neutrals?