New house, is wiring in garage good enough?
Mod note: member is in Canada
Hello all, need some advice please.
Just bought a new house and the main panel is in the house with a sub panel in garage.
I have a welder that requires 50amps 220v and a compressor that needs 20amp and 220v. Plus the lights and a 110v welder.
At my current house panel was in garage so it was a easy hook up. But I'm confused with the sun panel, wondering if the sun panel is receiving enough juice to run all this. The main breaker on sub panel appears to be 40amp and the breaker in house for garage appears to be 40amp.
My confusion is the wires, the wires appear to change somewhere. I have included pics of the setup. The first couple are panel in house feeding garage. The rest with be of panel in garage.
Any help would be great.
I did buy a new sub panel with new breakers for the setup I need to have, I'm just not sure if the wires going to garage are sufficient.
Hello all, need some advice please.
Just bought a new house and the main panel is in the house with a sub panel in garage.
I have a welder that requires 50amps 220v and a compressor that needs 20amp and 220v. Plus the lights and a 110v welder.
At my current house panel was in garage so it was a easy hook up. But I'm confused with the sun panel, wondering if the sun panel is receiving enough juice to run all this. The main breaker on sub panel appears to be 40amp and the breaker in house for garage appears to be 40amp.
My confusion is the wires, the wires appear to change somewhere. I have included pics of the setup. The first couple are panel in house feeding garage. The rest with be of panel in garage.
Any help would be great.
I did buy a new sub panel with new breakers for the setup I need to have, I'm just not sure if the wires going to garage are sufficient.
Last edited by Tolyn Ironhand; 08-13-17 at 07:11 PM.
#2
Welcome to the forums.
Your pictures didn't make it. http://www.doityourself.com/forum/el...-pictures.html
You are limited to the size of the breaker feeding the sub panel and the size of the wiring. 40A is certainly not going to be large enough for your application.
Your pictures didn't make it. http://www.doityourself.com/forum/el...-pictures.html
You are limited to the size of the breaker feeding the sub panel and the size of the wiring. 40A is certainly not going to be large enough for your application.
#4
Member
Thread Starter
Join Date: Aug 2017
Posts: 7
Received 0 Votes
on
0 Posts
The pics.
https://imgur.com/gallery/UrmVl
The wires from the panel don't seem to match what shows up in garage. Not sure I mentioned that.
https://imgur.com/gallery/UrmVl
The wires from the panel don't seem to match what shows up in garage. Not sure I mentioned that.
Last edited by ray2047; 08-13-17 at 08:16 PM. Reason: Fixed link
#5
The wire in the main panel is #6 and the wire in the conduit appears to be #8. The circuit is limited to 40 amps max. There must be a junction box where the wires changed. I would suspect the main panel feed goes to the kitchen perhaps an old feed to a range or oven.
#7
It really depends on your actual loads. People always say they have a 50 amp welder when really the welder only has a 50 amp plug on it. That actual settings and duty cycle of the welder will come into play when determining if the circuit will handle the load. The nameplate on the welder is worst case, full power, running everything, full duty.
You need to run a new feeder to the sub panel. On a side note: the 40 amp breaker in the sub panel is redundant. The feeder can be connected to the main lugs of the panel. (In the US, Canada may be different) That will open up 2 spaces for a 240 volt breaker.
You need to run a new feeder to the sub panel. On a side note: the 40 amp breaker in the sub panel is redundant. The feeder can be connected to the main lugs of the panel. (In the US, Canada may be different) That will open up 2 spaces for a 240 volt breaker.
#8
Member
Thread Starter
Join Date: Aug 2017
Posts: 7
Received 0 Votes
on
0 Posts
That's what I wondered. I couldn't figure out why the sub panel had a breaker for the main.
Also what size cable and types etc should I be running when I decide to tackle that crappy job?
My welder is a Lincoln 225 stick welder. Plate on it does say 50amp constant.
Also what size cable and types etc should I be running when I decide to tackle that crappy job?
My welder is a Lincoln 225 stick welder. Plate on it does say 50amp constant.
#9
Yes, but that would be at max power on the welder. Do you normally crank the welder on full power when welding? If so, then you will likely need a larger feeder to the garage.
#13
You could use 2-2-4-6 aluminum mobile home cable on as 90 amp breaker to a 100 amp main breaker panel in the garage. The MH cable can be direct buried without conduit but will need to be sleeved in conduit to where it enters the ground and from where it leaves the ground. Note: MH cable inside a structure must be in conduit all the way to the panel even if inside a finished wall.
Subpanel at garage will need a ground bar added. The neutral bar will not be bonded. You will need one or two ground rods at the garage connected to the subpanel ground bar with #6 copper.
Suggestions based on NEC not CEC. Your milage may vary.
Subpanel at garage will need a ground bar added. The neutral bar will not be bonded. You will need one or two ground rods at the garage connected to the subpanel ground bar with #6 copper.
Suggestions based on NEC not CEC. Your milage may vary.