I am in the process of adding a 50A sub-panel (GFCI) for hot tub to my main house panel. It is an older panel, Challenger SB10(20-20)CT Mod. 3 in the house. When I looked in the panel, it doesn't look like one can readily "tap" into it to add a sub-panel, please see attached image. Interestingly the panel doesn't even have a main breaker in the panel itself but does have on out at the meter. Any ideas as to the best way of adding said sub-panel in this scenario? Thank you in advance for any feedback.
 
Attached Images  
Sponsored Links
  #2  
Old 09-01-17, 12:47 PM
S
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 19,575
Received 94 Votes on 83 Posts
Welcome to the forums.

Other might be able to answer based on the name of the panel alone but I could benefit from a picture taken from further away.
 
  #3  
Old 09-01-17, 12:50 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 35 Votes on 27 Posts
If your main circuit breaker is at the meter then THAT is your "main" (more properly, service), panel. The electricians will need to see several more pictures of your installation to properly advice you. Both close-up and from enough distance to see how things are connected.
 
  #4  
Old 09-01-17, 12:56 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,943
Received 43 Votes on 41 Posts
You normally wouldn't tap into the panel feeder to add a subpanel, although that can sometimes be done. The usual way of adding a 50A subpanel would be to install a 50A double-pole breaker in the panel and feed the subpanel from that. If your panel has two open slots this is a relatively easy thing to do. If you don't have the open slots the project becomes more complicated.

If your panel by the meter has open slots that may be a better spot to feed the subpanel.
 
  #5  
Old 09-01-17, 01:38 PM
B
Member
Thread Starter
Join Date: Sep 2017
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
Thank you for the quick replies! It makes a lot more sense to add a breaker at the main service panel, thank you for that! After opening the panel there is an open slot for another breaker but now I'm concerned with the state of the main service panel. Please have a look at the attached picture, it appears to me that there has been some serious heat issues with the insulator melting. Should this be replaced?
 
Attached Images  
  #6  
Old 09-01-17, 03:36 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 35 Votes on 27 Posts
I agree, that looks nasty!

You MAY ( I don't know for certain) be able to have those bus bars alone be replaced (not a DIY job) and that would/should be significantly less expensive than a panel replacement.
 
  #7  
Old 09-01-17, 04:04 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,160
Received 1,114 Votes on 1,034 Posts
Welcome to the forums.

Good thing you checked now. It wouldn't have been much longer until that breaker completely fried.

I never had much luck getting replacement bus bars. It is possible although they may have to be ordered. As an electrician.... I will usually change the entire unit.
 
Attached Images  
  #8  
Old 09-03-17, 05:30 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,656
Received 86 Votes on 76 Posts
Any equipment with the Challenger name is obsolete and no longer available. Although the Eaton/Cutler-Hammer BR series breakers can be used in Challenger equipment and are identical to the old Challenger breakers, the old equipment and/or parts for it are no longer available.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: