Basement wet bar - circuits needed

Reply

  #1  
Old 09-07-17, 08:36 PM
4
Member
Thread Starter
Join Date: Mar 2007
Location: USA
Posts: 87
Received 0 Votes on 0 Posts
Basement wet bar - circuits needed

Hi all, I'm working on finishing my basement and am planning out the number of branch circuits that are needed. I'm planning to have a wet bar / kitchenette that will include a dishwasher, ice maker, microwave, and likely two under-counter fridges. Believe I can ignore the lights, as those can be included with a different circuit (the adjoining red room), so how many breakers should I plan for this area? The fridges I'm looking at do call for dedicated 15amp circuits in their installation manuals, so I guess that's two (I can't run one 20 amp?). I assume I need two 20 amp small appliance circuits , as I would in a standard kitchen. Can these appliance circuits be used for the other appliances - i.e. dishwasher, ice maker, microwave?

Thanks,
Guy
 
Sponsored Links
  #2  
Old 09-07-17, 08:42 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,610
Received 44 Votes on 39 Posts
Kitchen. An area with a sink and permanent provisions for food preparation and cooking.
Check with your local inspector as some think built in microwave makes it a kitchen. If not you don't need the 20amp SABCs and can share.
 
  #3  
Old 09-07-17, 08:53 PM
4
Member
Thread Starter
Join Date: Mar 2007
Location: USA
Posts: 87
Received 0 Votes on 0 Posts
I will have a sink, but loose the microwave and I'm good?

I was actually planning to leave a below-counter shelf with a receptacle at the back for a free standing microwave. I don't know what the definition of built in microwave is, but not sure it what I have planned would count. Either way, I can call the inspector...good call.
Thanks
 
  #4  
Old 09-08-17, 09:55 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,322
Received 112 Votes on 104 Posts
What's the wattage rating on the fridges? Standard-size fridges don't call for dedicated circuits, so I'm surprised the smaller under-cabinet ones do.
 
  #5  
Old 09-09-17, 06:35 AM
4
Member
Thread Starter
Join Date: Mar 2007
Location: USA
Posts: 87
Received 0 Votes on 0 Posts
The fridges are rated for 2.3 amps. I talked with the inspector and he didn't consider it a kitchen. I'm planning one general/small appliance circuit, one circuit for the two fridges (2.3amp each), one for the microwave (I don't know rating, but it's pretty high because it is also a convection oven)), one for the dishwasher (12amp), and one shared by the garbage disposal (9amp) and ice maker (~2.5amp). So total of five circuits, and I'll likely run them all as 20 amp circuits.

Thanks,
Guy
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: