20 amp female 3 pins to 30 amp male three pins.

This male three pins plugs into my clothes drier, 30 amps:

https://plus.google.com/photos/photo...2a_s__uPeD_AEr


I want to plug this

https://plus.google.com/photos/photo...false&iso=true

20 amp 3 pins extension cord into same recepticle for the 30 amp see above.

Is there an adapter for this? 20 amp female 3 pins to 30 amp male three pins.

Extension cord is for welder rated at 20 amps.

Thanks!

 
Sponsored Links
  #2  
Old 09-10-17, 04:37 PM
L
Member
Join Date: Nov 2015
Posts: 1,322
Received 41 Votes on 38 Posts
Are you sure you have the correct extension cord for your welder?
That is 120V 20A plug. Not a 240V. With welders generally being 240V, I think you might have a wrong extension cord. If your welder really is a 120V 20A, you are better off using kitchen outlets, which are supposed to be on 20A. You probably will have to change existing outlet with 20A since most homes only have 15A outlets.

Your extension cord plugs on this type of outlet.
https://upload.wikimedia.org/wikiped...with_label.jpg
 
  #3  
Old 09-10-17, 07:24 PM
C
Member
Thread Starter
Join Date: Mar 2008
Posts: 6
Received 0 Votes on 0 Posts
This is spec:

"This Lincoln Electric Easy MIG 140 Flux-Core/MIG Welder uses common 120V power and is a fine choice for home projects, farm repairs or basic auto body work."


FREE SHIPPING — Lincoln Electric Easy MIG 140 Flux-Core/MIG Welder — 115V, 140 Amp, Model# K2697-1 | MIG Flux Core Welders| Northern Tool + Equipment


Don't want to be pulling 20A thru a 15A plug. Would make more sense to pull 20A thru 30A recepticle, with proper adapter...
 
  #4  
Old 09-10-17, 07:43 PM
L
Member
Join Date: Nov 2015
Posts: 1,322
Received 41 Votes on 38 Posts
Don't want to be pulling 20A thru a 15A plug.
You won't be if you change the outlet on 20A circuit to 20A.

Would make more sense to pull 20A thru 30A recepticle, with proper adapter...
This is illegal and therefore, proper adapter does not exist.
Also, 3 prong dryer outlet does not have a neutral. It shares ground wire as neutral, which is illegal now.
 
  #5  
Old 09-11-17, 09:00 AM
J
Member
Join Date: Aug 2017
Location: United States
Posts: 21
Received 0 Votes on 0 Posts
I have a similar welder (Lincoln SP140). Your dryer is 240v and your welder is 120v. There is no adapter and trying to make one is a very bad idea.

If you're doing small work, you can get a 15 to 20 amp adapter to use the welder on a normal 15 amp outlet, but it cannot be used on the highest setting without tripping the breaker. You'd be limited to about 1/8" thick steel before it'll trip the breaker. My manual shows the adapter and the max settings for 15 amp input. If yours isn't clear, call Lincoln, their tech help is pretty good.

If you'll be needing the welder at higher settings, your only option would be a 120v 20 amp circuit. I have seen many houses wired with 12 gauge wiring and 20 amp breakers, but use 15 amp receptacles. If that's the case, swapping a 20 amp receptacle would be easy. Just don't do that unless you know that it's 12 gauge wiring.
 

Last edited by JoeWilson; 09-11-17 at 11:56 AM.
  #6  
Old 09-11-17, 09:36 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,367
Received 48 Votes on 39 Posts
Also, 3 prong dryer outlet does not have a neutral. It shares ground wire as neutral, which is illegal now.

I prefer to say that it shares neutral as ground OR the grounding is through the neutral as the neutral conductor in a NM cable must be insulated.
 
  #7  
Old 09-11-17, 03:13 PM
C
Member
Thread Starter
Join Date: Mar 2008
Posts: 6
Received 0 Votes on 0 Posts
I'll go with the recc for light welding with 15-amp adapter.

No way to know what gauge wiring is. House is 50 years old.

What do you think it would cost to wire in a 20-amp breaker at the service panel?
 
  #8  
Old 09-11-17, 03:18 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
What do you think it would cost to wire in a 20-amp breaker at the service panel
DIY or hire an electrician?
 
  #9  
Old 09-11-17, 04:35 PM
L
Member
Join Date: Nov 2015
Posts: 1,322
Received 41 Votes on 38 Posts
I wouldn't recommend running welder on 15A circuit. Even if the welder is pulling less than 15A, there will be some voltage drop due to high load.
It will run ok on low settings, but may have difficulties welding on higher settings.
Even Harbor Freight 120V welder with 15A plug says use it on 20A circuit.

It might be ok if 15A outlet you are tapping into isn't too far from the breaker, but cannot always guarantee that.
 
  #10  
Old 09-11-17, 09:22 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Received 0 Votes on 0 Posts
Why don't you use the washer outlet? Replace it with a 20A GFCI if it isn't already and you'll be good to go.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: