3/4" Schedule 80 fill rate

Reply

  #1  
Old 09-19-17, 10:13 AM
Member
Thread Starter
Join Date: Sep 2017
Posts: 1
Received 0 Votes on 0 Posts
3/4" Schedule 80 fill rate

I have a detached garage that already has a short (15 feet) section of 3/4" Schedule 80 PVC that is buried under concrete leading to the LB that enters the garage.

Based on the conduit fill charts I can only fit (3) #6 AWG in that conduit. The rest of the run to the main panel is 3/4" Schedule 40 which allows (4) #6 AWG conductors.

Because of that small section of Sch 80 I chose to pull 8/8/8/10 feeders to the garage and it was a piece of cake. So much that I am now wondering if I should pull 6/6/6/10 instead to maximize my potential at the subpanel.

If the fill chart says max of (3) #6 conductors, does that mean there is no room for the #10 AWG ground? Or does that just mean no room for a 4th #6 AWG?
 
Sponsored Links
  #2  
Old 09-19-17, 11:06 AM
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,149
Received 21 Votes on 17 Posts
The charts are a quick guide line. If using THHN/THWN wire using the Southwire Mil size for #6 and #10 Cu, three #6 and one #10 will fit in 3/4 Sch 80 PVC. I get .1637 for the four wires and the NEC chart list 3/4" Sch 80 fill at 40% as .164. So it just does fit.

Edit: A moment of pause, I used the wrong size for the #10. Will recalculate.

Edit: The issue is South has two different insulation thicknesses on the #10 and one puts the total at .1637 and the other at .166 which is a very small amount over the .164. Bottom line I wouldn't worry about it. If you are using THHN/THWN I say go ahead with the 6-6-6-10 in the Sch 80.
 
  #3  
Old 09-19-17, 02:30 PM
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,149
Received 21 Votes on 17 Posts
It just dawned on me that the two size differences for the #10 is solid vs. stranded. The stranded is the larger.
 

Last edited by pattenp; 09-19-17 at 04:48 PM.
  #4  
Old 09-19-17, 04:22 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,933
Received 54 Votes on 47 Posts
Using the NEC code book tables, the area available for conductors in 3/4" Sch 80 PVC is 0.164 (40% fill for over 2 wires)
#6 THHN/THWN wires are 0.0507
#10 THHN/THWN wires are 0.0211

0.0507 x 3 = 0.1521 + 0.0211 = 0.1732

You are 0.0092 over. IMO I would install the #6
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: