Guage of wire for T8 tombstones

Reply

  #1  
Old 09-25-17, 10:03 AM
M
Member
Thread Starter
Join Date: Sep 2017
Location: usa
Posts: 2
Received 0 Votes on 0 Posts
Guage of wire for T8 tombstones

I am rewiring old fixtures for LED and have to swap out shunted to non-shunted tombstones. My old tombstones are wired with a solid aluminum wire.

I have 2 bulbs in each fixture and since they are wired on one side, I wanted to daisy chain the 2 non-shunted tombstones in parallel and then splice it to the inbound 110V coming into the fixture.

The new Leviton 13180-U tombstones call for 18AWG - but everything I read says that 18AWG is used primarily for 24v/48v applications and that's really my worry.

Can I safely use 18AWG wire to run 110v into and between the tombstones?

Thanks.
 
  #2  
Old 09-25-17, 10:07 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,854
Received 1,335 Votes on 1,234 Posts
Welcome to the forums.

The fixture wire is #18 but the insulation is special high heat type and is allowed to be used in those types of fixtures.

If you used generic wiring you would need #14 THHN solid.
What happened to the old wiring..... or the wire from an old ballast.
That's what I use.
 
  #3  
Old 09-25-17, 04:03 PM
M
Member
Thread Starter
Join Date: Sep 2017
Location: usa
Posts: 2
Received 0 Votes on 0 Posts
thanks for the info, that's what I needed/ The old ballast wire is all bent and looped and I wanted to pre-wire on the ground and just swap out the tombstones. There is a big price difference in the single vs 2 sided tubes, otherwise i could keep with the old tombstones and just cut out the ballast..
 
 