Need help with sub panel location

I've been racking my brain on this. Building a 500 sq/ft addition. Ran 6/3 wire to the addition side of the house with about 15ft of slack. Trying to decide on putting the sub panel in the basement near the crawl space opening. https://prnt.sc/gq4m3q running the wires up and in from the floor.

Or....

Put it in the 2x6 wall in the spare room in the addition?
 
Attached Images  

Last edited by ray2047; 09-26-17 at 06:04 PM. Reason: Add image.
Sponsored Links
  #2  
Old 09-27-17, 07:59 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 43 Votes on 41 Posts
Yeah it looks like the sub can probably go there, but that shelving unit has to move. Panel clearance is 30" wide in front of the panel (the panel does not need to be centered in the 30"), and 36" out from the face of the panel. The highest breaker must be less than 6'-7" from the floor. Basically you need to be able to slide a refrigerator box up to the panel without hitting an obstruction. Storage of any kind is not permitted in front of a panel.
 
  #3  
Old 09-27-17, 10:17 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,638
Received 83 Votes on 73 Posts
I'd put the subpanel in the basement.
 
  #4  
Old 09-27-17, 02:18 PM
J
Member
Thread Starter
Join Date: Sep 2017
Location: United States
Posts: 3
Received 0 Votes on 0 Posts
Okay new location possibility...

https://imgur.com/a/XLLCW

The resolution of the attached image is horrendous. That's why I'm linking the imgur link.
 
Attached Images  

Last edited by jayjr1105; 09-27-17 at 03:12 PM. Reason: Add image.
  #5  
Old 09-27-17, 03:43 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,595
Received 200 Votes on 178 Posts
24" is not enough space in front of a panel. 30" is minimum. The laundry tub is fine, the drain is not.
 
  #6  
Old 09-27-17, 04:31 PM
J
Member
Thread Starter
Join Date: Sep 2017
Location: United States
Posts: 3
Received 0 Votes on 0 Posts
Hrmm. I was afraid so. I guess the original location it is then. Unless I move back into the addition itself.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: