15 AMP some new outlet


  #1  
Old 10-06-17, 04:41 AM
M
Member
Thread Starter
Join Date: Oct 2017
Location: Australia
Posts: 1
Received 0 Votes on 0 Posts
15 AMP some new outlet

Hi , we have a workshop with both three phase and single phase power source
wiring is really old , we are installing some new machinery which is recommended for 15 AMP power source ,
My question is should i wire a single cable and single circuit breaker for each machinery ??
or wire a three phase cable with 68 amp three phase circuit breaker from main panel and get 3 amps outlet single phase of each phase for each machinery ?
distance is around 20 meter from panel

Thanks for help in advance
 
  #2  
Old 10-06-17, 10:26 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 70,129
Received 2,965 Votes on 2,675 Posts
Welcome to the forums from down under.

Each single phase machine should have its own line and single 15A breaker.

If you ran a three phase cable and then just branched off of each phase to a receptacle..... the receptacles would be protected at 68A each which would not be allowable.
 
  #3  
Old 10-06-17, 01:46 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,575
Received 15 Votes on 13 Posts
There is more to 3-phase than mentioned. You need to be sure you have 120 volts and not 208 volts between the the hot you run and neutral. Your question shows lack of experience. I'd suggest you hire an electrician.
 
  #4  
Old 10-06-17, 01:54 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 70,129
Received 2,965 Votes on 2,675 Posts
Good points Ray.

Power in Australia is 50Hz - Single phase 240v and 3-phase 415v.
I don't believe there is 120v in use in Australia..... just 240v to ground.

But.... three phase voltages can be much higher than 240v per leg so caution in connecting any equipment needs to be used.
 
  #5  
Old 10-07-17, 07:47 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,930
Received 215 Votes on 198 Posts
The published or official voltage of a 3 phase circuit is the highest voltage between any two conductors (not counting an equipment grounding condudtor), which would be the voltage between the A leg and the B leg, the voltage between the B leg and the C leg, and the voltage between the C leg and the A leg, all three of which voltages should be the same give or take a volt or two.

Check each machine to be sure the voltage it needs is the same as the voltage provided by your system.

Not all 3 phase systems have a neutral (groiunded conductor) as a fourth conductor (where an equipment grounding conductor would be a fifth conductor).. A "wye" or "star" system has such a neutral where the voltage between any of the three phase lines and the neutral is the same.

The aforementioned 415 volt 3 phase system has 415 volts phase to phase e.g. A to B and 240 volts phase to neutral.
 
 