junction box ground question

Reply

  #1  
Old 11-02-17, 08:21 AM
Member
Thread Starter
Join Date: Jan 2014
Posts: 11
Received 0 Votes on 0 Posts
junction box ground question

I have a junction box with six 14/2 runs coming in. What do I do with the grounds? Do splice them all together and pigtail to a ground screw? Because that would be a splice of seven wires which seems like a lot. This is not a new addition so I can not leave a long wire at the end and use a green wire nut. Do all of the grounds have to be splice together or can they be separated and have two pigtails to the same ground screw?
 
Sponsored Links
  #2  
Old 11-02-17, 08:49 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Either of your suggestions is ok.
 
  #3  
Old 11-02-17, 08:58 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,956
Received 33 Votes on 28 Posts
Only one wire per screw head. You cannot have two wires under the same screw. You can jumper two smaller groups together and then to the screw.
 