20a gfci on 15a circuit, no T
Old 11-07-17, 07:20 PM
Q
Received 1 Vote on 1 Post
I need to relaxed a bathroom gfci on a 15a circuit. I have a spare gfci but it says it's rated for 20a. However, it just has flat receptacle pins, not a T like a normal 20a plug.
is it ok to install this?
Because it's missing a T receptacle, you could never plug a 20a device into it but even if you could, the breaker would trip?
Old 11-07-17, 09:58 PM
A
Received 81 Votes on 73 Posts
Canadian rules are a bit different. In the US a bathroom circuit feeding a receptacle has to be 20amp.
A 15amp receptacle and GFCI is normally rated 20amp feed-through. That's probably what you are seeing.
Old 11-08-17, 01:23 AM
Q
I think it's new renovated bathrooms.
this is existing wiring, the building is 100 years old,
Bathroom maybe renovated in 1970 when 15a was the norm, so it's grandfathered in.
Old 11-08-17, 06:43 AM
A
Received 215 Votes on 198 Posts
The 15 amp branch circuit breaker would not (should not) trip unless the total power drawn by all lights and appliances on that circuit exceeded 15 amperes.
A 15 amp ground fault circuit interrupter receptacle unit might not trip if the total power drawn through its receptacles and other receptacles daisy chained through it (pass-through) exceeded 15 amps or even 20 amps.
Thus a GFCI unit is not for overcurrent protection unless it is specifically described, listed, or advertised as such e.g. is a GFCI panel breaker.
Old 11-08-17, 07:11 PM
Q
So no problem connecting the 20a gfci then?
if it was a true 20a it would have the t slot on the receptacle.