208 Volt Single Phase
#1
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 3
Received 0 Votes
on
0 Posts
208 Volt Single Phase
I come here in hopes I can get a quick answer before buying this equipment. I am interested in a Hobart food Mixer that is rated at 208 Volt, Single phase. I would like to use it at home. Is it possible, or do I need an UP converter to bring it to 220 volt, etc? The 208 volt tag does not say 208-240, just straight 208 volt. I am hoping I can use it at home, cross my fingers!!
Any help would be mist appreciated!
Thank you
Ed
Any help would be mist appreciated!
Thank you
Ed
#2
Welcome to the forums.
We have 240v in our homes in the U.S. not 220v.
208v is what is obtained from three phase service.
That Hobart machine should run on 240v just fine.
You can always post the equipment model number for further info and 100% confirmation.
We have 240v in our homes in the U.S. not 220v.
208v is what is obtained from three phase service.
That Hobart machine should run on 240v just fine.
You can always post the equipment model number for further info and 100% confirmation.
#4
Usually it can be found in the technical info on the appliance.
That's why I was looking for a model number.
That's why I was looking for a model number.
#5
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,340
Received 0 Votes
on
0 Posts
208-V, single-phase is commonly encountered in the U.S. - mainly in commercial situations. It is derived from a delta-connected, 3-phase utility xfmr. The connection also provides 120-V single phase from a center-tapped phase winding.
Many appliances are rated 240/208V. Call the manufacturer and verify that 240V is OK. It probably is - and will draw a bit lower amps and run cooler than at 208.
Many appliances are rated 240/208V. Call the manufacturer and verify that 240V is OK. It probably is - and will draw a bit lower amps and run cooler than at 208.
#6
It is derived from a delta-connected, 3-phase utility xfmr.
A wye connected 3 phase service will be 208 volts phase to phase, 120 volts phase to ground on all phases.
#7
If it is rated for 208 volts and not 240 volts also then 240 volts is an overvoltage condition that can shorten its life.
Find out what voltage it is rated for rather than just try things.
Find out what voltage it is rated for rather than just try things.
#8
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 3
Received 0 Votes
on
0 Posts
I think I was told that if its rated for 208 only, that I need a step-down transformer to be used on 240: 1 Phase Buck & Boost Step-Down Transformer - 236V Primary - 208V Secondary at 26.6 Amps - 50/60Hz - Larson Electronics
#9
Typically, voltage +/- 10% is considered within tolerance and is OK. I would just call Hobart and check with them. If they do say it needs to be 208 then yes, you will likely need a Buck/Boost xfmr.