208 Volt Single Phase

I come here in hopes I can get a quick answer before buying this equipment. I am interested in a Hobart food Mixer that is rated at 208 Volt, Single phase. I would like to use it at home. Is it possible, or do I need an UP converter to bring it to 220 volt, etc? The 208 volt tag does not say 208-240, just straight 208 volt. I am hoping I can use it at home, cross my fingers!!

Any help would be mist appreciated!

Thank you

Ed
 
Sponsored Links
  #2  
Old 12-10-17, 01:03 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,121
Received 374 Votes on 351 Posts
Welcome to the forums.

We have 240v in our homes in the U.S. not 220v.
208v is what is obtained from three phase service.
That Hobart machine should run on 240v just fine.

You can always post the equipment model number for further info and 100% confirmation.
 
  #3  
Old 12-10-17, 01:31 PM
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 3
Received 0 Votes on 0 Posts
Yes, but my Hobart's tag description is single phase, 208 Volt, and not a 3 phase. Therefore, it will run on my residential 240 volt system?

Thank you much!

Ed
 
  #4  
Old 12-10-17, 02:22 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,121
Received 374 Votes on 351 Posts
Usually it can be found in the technical info on the appliance.
That's why I was looking for a model number.
 
  #5  
Old 12-10-17, 02:50 PM
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,340
Received 0 Votes on 0 Posts
208-V, single-phase is commonly encountered in the U.S. - mainly in commercial situations. It is derived from a delta-connected, 3-phase utility xfmr. The connection also provides 120-V single phase from a center-tapped phase winding.

Many appliances are rated 240/208V. Call the manufacturer and verify that 240V is OK. It probably is - and will draw a bit lower amps and run cooler than at 208.
 
  #6  
Old 12-10-17, 03:13 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,965
Received 59 Votes on 52 Posts
It is derived from a delta-connected, 3-phase utility xfmr.
Normally a Delta connected 3 phase service is 240 volts phase to phase, while A and C phase is 120 volts to ground. B phase is your high leg and will be about 208 phase to ground.

A wye connected 3 phase service will be 208 volts phase to phase, 120 volts phase to ground on all phases.
 
  #7  
Old 12-10-17, 03:50 PM
Member
Join Date: Mar 2010
Location: USA
Posts: 3,550
Received 20 Votes on 20 Posts
If it is rated for 208 volts and not 240 volts also then 240 volts is an overvoltage condition that can shorten its life.

Find out what voltage it is rated for rather than just try things.
 
  #8  
Old 12-10-17, 04:10 PM
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 3
Received 0 Votes on 0 Posts
I think I was told that if its rated for 208 only, that I need a step-down transformer to be used on 240: 1 Phase Buck & Boost Step-Down Transformer - 236V Primary - 208V Secondary at 26.6 Amps - 50/60Hz - Larson Electronics
 
  #9  
Old 12-10-17, 04:32 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,965
Received 59 Votes on 52 Posts
Typically, voltage +/- 10% is considered within tolerance and is OK. I would just call Hobart and check with them. If they do say it needs to be 208 then yes, you will likely need a Buck/Boost xfmr.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: