Ground for outbuilding electric


  #1  
Old 12-13-17, 04:21 PM
M
Member
Thread Starter
Join Date: Jul 2015
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ground for outbuilding electric

Ok, I'm running power to an out building/shed. I'm coming off of my meter box with a 40 amp service. My question is, in my breaker box inside my building do I need to bond the neutral and ground?
 
  #2  
Old 12-13-17, 05:11 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
Are you coming out of the meter or the panel?

I doubt through in the meter are good for a small conductor like a #8.
 
  #3  
Old 12-13-17, 05:11 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
Any service would need to be grouped near the existing set ice.
 
  #4  
Old 12-13-17, 05:30 PM
M
Member
Thread Starter
Join Date: Jul 2015
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Is not the breaker box in the house. Is coming off the box that's mounted on the pole under my meter.
 
  #5  
Old 12-13-17, 07:05 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
You have a pole mounted service with a disconnect panel. One breaker feeds the house and another.... 40A.... will feed the outbuilding. That panel in that building is considered a sub panel and the grounds and neutrals are kept separate. You will need four wire cable between that main disconnect panel and the sub panel. You will need a ground rod at that building that will connect to the ground block in the sub panel.
 
  #6  
Old 12-13-17, 07:28 PM
M
Member
Thread Starter
Join Date: Jul 2015
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the reply. Will I still need to connect my ground in my service disconnect panel too?
 
  #7  
Old 12-13-17, 09:33 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
The service disconnect and the building with the sub panel need to be connected with four wire cable. Two hots, a neutral and a ground.
 
 