I am helping a friend out and installing a 100amp subpanel in his garage 6 inches from the back of his 200amp main panel outside (Southern California). we want to monitor the amps used and whatnot for the whole panel so I bought this:
https://www.amazon.com/ELEGIANT-80-2...3Y83HT4JTJ1XJ6
My question, is can you permanently mount this in the subpanel, or does it have to be outside the subpanel in a separate box? the leads off the CT are pretty short and i would run the main legs through the CT. I want to be safe and to code. I haven't found anything about this sort of thing, which makes me believe its not ok.
https://www.amazon.com/ELEGIANT-80-2...3Y83HT4JTJ1XJ6
My question, is can you permanently mount this in the subpanel, or does it have to be outside the subpanel in a separate box? the leads off the CT are pretty short and i would run the main legs through the CT. I want to be safe and to code. I haven't found anything about this sort of thing, which makes me believe its not ok.
#3
Welcome to the forums.
There's a fine line here. Code says panels shouldn't be modified. Covers are not specifically mentioned. I think those breaker locks/interlocks that bolt into the cover are iffy.
In my opinion.... it is not customary to modify a panel cover and install that meter in the cover. I would recommend installing it in a separate enclosure also.
They don't discuss connection to the panel with that unit. It needs to be connected to a 2P circuit breaker as it needs 240v.
I have similar devices on some of my pro equipment. I connect directly to the incoming lines that supply the panel but I use two fully insulated fuseholders and 5A 250v fuses for protection. This is my method. I'm not recommending it to you.... just mentioning it.
There's a fine line here. Code says panels shouldn't be modified. Covers are not specifically mentioned. I think those breaker locks/interlocks that bolt into the cover are iffy.
In my opinion.... it is not customary to modify a panel cover and install that meter in the cover. I would recommend installing it in a separate enclosure also.
They don't discuss connection to the panel with that unit. It needs to be connected to a 2P circuit breaker as it needs 240v.
I have similar devices on some of my pro equipment. I connect directly to the incoming lines that supply the panel but I use two fully insulated fuseholders and 5A 250v fuses for protection. This is my method. I'm not recommending it to you.... just mentioning it.
#4
Forum Topic Moderator
I too would recommend a separate box. At some point in time, it'll die and will need to be replaced - and you'll end up having to cover a large cutout in the panel cover.
I would use something like this
Either in a 4x4 or 6x6 size depending on the size of the meter. Connect it to the panel with a short nipple.
It looks like you can easily extend the wires on the CT transformer.
I would use something like this
Either in a 4x4 or 6x6 size depending on the size of the meter. Connect it to the panel with a short nipple.
It looks like you can easily extend the wires on the CT transformer.