Breaker tripped once with new electrical installation, but no short found.

We are converting a former garage space into an office. We hired a general contractor to frame out the new office, then I went through and ran the electrical throughout the room, then the contractor came back and put the drywall up and finished the walls. This last week I have been installing all the lights, outlets, ect. When I ran the electrical, I installed a small load center just outside of the office for the various circuits of the new office. On one 20 amp circuit that supplies power to wall outlets on 3 of the 4 walls, I wired and installed all the outlets, then turned the breaker on and it instantly tripped. I then removed all the outlet covers and looked closely for and issues. I found none, nothing even questionable. I then checked the circuit for a short between the hot and neutral/ground wires and found none. There is no longer a short. Puzzled and worried, I pulled out each outlet and inspected all outlets, boxes, and wiring for any possible signs of a short, and found none. I then put everything back together and once again turned the breaker on. This time no problems. I put my clamp meter on the wire coming out of the breaker and measured no current.
Each outlet works properly. I then plugged in 2 electric heaters drawing a total of 16 amps and let them run for 1 hour, no problem. The only thing I can think of is when the contractor hang the drywall he may have screwed into a wire. Either way, there was a short and now there is not, what would you suggest I do.
 
Sponsored Links
  #2  
Old 12-22-17, 09:00 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,967
Received 59 Votes on 52 Posts
Sometimes a breaker will trip when turned on, even when there is no fault. I have seen it many times. If the breaker reset I suspect it is OK.

The only thing I can think of is when the contractor hang the drywall he may have screwed into a wire.
If the cables were installed properly and protected by keeping them 1 1/4" away from the stud face, or using nail plates, there should be little chance that a cable was hit. That said, it still could happen if the drywall hanger used overly long screws.

I should ask, is this a standard breaker or a GFCI or AFCI breaker? Did the breaker make a big pop/spark when it tripped?
 
  #3  
Old 12-22-17, 09:11 PM
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 6
Received 0 Votes on 0 Posts
Thanks for the reply.
The breaker definitely made a violent pop.
I was sure to drill the holes through the center of the studs, if not a hair to the rear of the stud, as the back of the studs will not be finished.
Another thought, is it possible to tighten the wire clamps in the boxes to the point they can cause a short? I had a helper that was stripping the wire back and tightening them in the clamps.
 
  #4  
Old 12-22-17, 09:15 PM
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 6
Received 0 Votes on 0 Posts
Standard breaker, not GFCI.
 
  #5  
Old 12-22-17, 09:27 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,493
Received 33 Votes on 25 Posts
"... is it possible to tighten the wire clamps in the boxes to the point they can cause a short?"

Definitely possible.
 
  #6  
Old 12-22-17, 09:41 PM
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 6
Received 0 Votes on 0 Posts
Well, seeing as there is no detectable short at this point, is there any fancy way of testing the circuit?
If there is a damaged wire, will there be a different voltage drop at a load placed at the end of the circuit, then if the wiring was undamaged? I mean, if there was a short initially, and the wire partially burned away, causing the short to open, the wire diameter will be reduced where it is burned. If I placed the heaters on the last outlet on the circuit, and measured the voltage at the heaters, will the voltage drop be greater then on a healthy circuit?
 
  #7  
Old 12-22-17, 09:47 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,493
Received 33 Votes on 25 Posts
I don't know of any sure fire method to find the fault, if indeed there is one. Visual inspection of the clamps and cable should show a burn mark if that was the cause of the breaker tripping initially. That it no longer trips tells me the original fault had to have burnt away about the same time as the breaker tripping. Is it still a hazard? Maybe, I don't know.

Wish I had better news.
 
  #8  
Old 12-22-17, 09:54 PM
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 6
Received 0 Votes on 0 Posts
I told the owner about this problem, and seeing that the walls and finished and painted, he does not want to open them back up.
One thing I did before I left was replace the 20 amp breaker with a 15 amp one. My theory was if the short does return, the breaker would be easier to trip.
 
  #9  
Old 12-22-17, 10:41 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,230
Received 379 Votes on 356 Posts
There is a way to try to find the short. You'd need a megger. It's a piece of test equipment that sends high voltage down the wire and checks for insulation breakdown. It will measure a "near short" location causing an overall low resistance measurement. They are bucks. The one I borrow is over $1500. Usually larger electrical contractors will have them.
 

Last edited by PJmax; 12-22-17 at 10:56 PM.
  #10  
Old 12-23-17, 06:42 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,967
Received 59 Votes on 52 Posts
I told the owner about this problem,
I thought you were the owner. Are you a just the general contractor?

One thing I did before I left was replace the 20 amp breaker with a 15 amp one. My theory was if the short does return, the breaker would be easier to trip
An AFCI breaker would be better.

If you open each box you might be able to see some black marks on the cable clamp if that was the cause of the short.
 
  #11  
Old 12-24-17, 01:46 PM
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 6
Received 0 Votes on 0 Posts
I am the owners employee.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: