Advice on electrical service to shed

This is probably a topic that's been brought up over and over again...

I've dug trenches and buried conduit for outbuildings in the past -- installed subpanels to both my previous houses' workshops / sheds. However, I recently got married and we moved into a little larger place that has a pretty built out backyard, complete with a pool and very large pool deck. The scenario I have is -- there's a shed that I'd like to use as a little workshop on the property, comparable to the size of the ones I've had at my previous houses. It has no electricity, other than what I'm using right now which is a long extension cord. There's currently a GFCI mounted on the pool deck, about 20 feet from the shed that's on it's own, dedicated 20A circuit breaker from the main panel. It services nothing else and is fed via 1/2" PVC conduit that runs under a bunch of concrete and the deck. When I say under a bunch of concrete, I mean replacing it with something larger would require me tearing up my pool decking, cutting two sidewalks, part of a driveway, etc. Ideally, I'd love to run 1 or 1 1/2" conduit from the main panel but have the same situation so that's not a very simple solution. I have wired the building with 10 outlets, 2 interior shop lights and 2 exterior motion sensing floodlights for the yard / driveway and everything's brought back to a very small GE main lug subpanel with 1 15A (lighting) and 5 20A breakers in it, which I'll very likely NEVER use all of. This was wired for convenience outlets, maybe in the summer running a small window unit air conditioner and a few small power tools (drill, battery charger, etc and that's about it . The question I have is would it be feasible to repurpose the 1/2" conduit and run conduit from that junction box over to the shed, pulling 3 of the 12ga wires out and replacing with 10ga? Or am I being overly optimistic? I would say the run is somewhere between 50 and 100' total, but not completely sure of the path it takes so can't be certain on an exact distance.

Also, would it be stupid to just put 30A service out to this building?

Thank you in advance.
Matt
 
Sponsored Links
  #2  
Old 12-28-17, 02:46 PM
kish2554's Avatar
Member
Thread Starter
Join Date: Jan 2010
Location: Fort Worth, TX
Posts: 46
Received 0 Votes on 0 Posts
The other question I had was....or do I dare trying to run 3 8ga wires and 1 10ga wire through that existing conduit? I know probably a horrible idea.
 
  #3  
Old 12-30-17, 06:59 AM
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,182
Received 25 Votes on 20 Posts
1/2" conduit can handle about 8 #12's, or 5 #10's or 3 #8's of THHN. 3 #8's + 1 #10 is possibly too much. Plus if you are trying to place over 3 current carrying conductors in conduit you will need to derate the amp capacity. Also putting 30A to the outbuilding is not stupid. The power needed all depends on what is being run at one time that consumes the most power.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: