Calculation of panel amps usage


  #1  
Old 12-24-17, 03:21 AM
Q
Member
Thread Starter
Join Date: Jun 2014
Location: Canada
Posts: 1,657
Received 1 Upvote on 1 Post
Calculation of panel amps usage

My panel is full and I wabt to replace a few spots with quads and tandems to add another circuit or two.
how can I calculate the amperage requirements so that it's not overloaded? It's a 100 amp Commander panel (challenger, Eaton, cutler H now).

Also, can I put a clamp meter on the main panel wire? It's a sub panel so I can switch it off first and measure at a few points during the day.
 
  #2  
Old 12-24-17, 05:29 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
You perform a demand load calculation. There are several available online.
 
  #3  
Old 12-26-17, 12:09 PM
Q
Member
Thread Starter
Join Date: Jun 2014
Location: Canada
Posts: 1,657
Received 1 Upvote on 1 Post
Is there a demand load for each side of the panel?
On a 100a breaker, do I only load 50 on each side?
What if I get it unbalanced somehow?
 
  #4  
Old 12-26-17, 12:20 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
The demand load calculation is for the panel.

On a 100 amp panel you can get 100 amps from either or both sides of the panel.
 
  #5  
Old 12-26-17, 04:29 PM
Q
Member
Thread Starter
Join Date: Jun 2014
Location: Canada
Posts: 1,657
Received 1 Upvote on 1 Post
Does that mean you can actually have up to 200 a total usage? Ignoring 80% rules and such...
 
  #6  
Old 12-26-17, 04:36 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 15,990
Received 84 Upvotes on 76 Posts
When we miscalculated whole house generator sizing for a panel we often had to amp test the mains coming into the panel... Clamp meter them with every single thing on in the home. Vacuums hair dryers etc.. Often on a 200 amp panel we got a meeker 50 - 60 amps a leg...
 
  #7  
Old 12-26-17, 05:32 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,523
Upvotes: 0
Received 277 Upvotes on 253 Posts
A 100 amp 120/240 volt service can give you up to 200 amps of 120 volt power or up to 100 amps of 240 volt power or different combinations not exceeding 100 amps on any leg.

1. You follow the rules for the load analysis. One set is at the back of the NEC.
2. The rules tell you the numbers to use for continuous loads such as air conditioners and intermittent heavy loads such as clothes dryers.
3. The result of the load analysis is the panel size and service size (in amps) you need.
4. You should balance as best as you can the 120 volt circuits on the two hot legs.
5. As a rule of thumb each branch circuit should have continuous load limited to 80% of the circuit rating (its breaker rating).
6. The entire system is de-facto limited to a continuous load of 80% of the service load because the main breaker is assumed to have that limit. In practice you will rarely hit that limit.
7. Most of the time the load in effect will be far less than the limit, for example 50-60 amps a leg for a home with a 200 amp service and most of the load spoken for (as opposed to still in the future).
 

Last edited by AllanJ; 12-26-17 at 06:00 PM.
  #8  
Old 12-26-17, 06:35 PM
Q
Member
Thread Starter
Join Date: Jun 2014
Location: Canada
Posts: 1,657
Received 1 Upvote on 1 Post
So, when you put in a 2 pole 240v breaker on the right side of the panel, it's actually balanced straight away since it uses both legs?
 
  #9  
Old 12-26-17, 07:07 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
Correct. Unless it is a 120/240 volt load (like a 4 wire feed to a range or dryer) there will be some imbalance there.

Think of it in watts.
100 amps @ 120v = 12000 watts x per leg (2) = 24000 watts total.
100 amps @ 240 volts (both legs) = 24000 watts.

They are the same total. Your max load can only be 24000 watts on a 100 amp panel.
Next we'll talk about the size of the transformer feeding your home.
 
  #10  
Old 12-27-17, 10:11 AM
Q
Member
Thread Starter
Join Date: Jun 2014
Location: Canada
Posts: 1,657
Received 1 Upvote on 1 Post
I'm getting 25,600W on my load demand calculation but I'm pretty sure the panel is never using that much.
1150sq ft
Heaters 11500W
Range cooker 4100W
Water heater 4500W
Clothes dryer 5600W
Portable AC running on 15A receptacle during some days in summer
 
  #11  
Old 12-27-17, 06:53 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
What is the heaters? Base board or one unit?
 
  #12  
Old 12-27-17, 11:26 PM
Q
Member
Thread Starter
Join Date: Jun 2014
Location: Canada
Posts: 1,657
Received 1 Upvote on 1 Post
Baseboard
The range says 49.4 amps on it but I'm pretty sure it never uses the full amount.
 
  #13  
Old 12-28-17, 02:58 PM
Q
Member
Thread Starter
Join Date: Jun 2014
Location: Canada
Posts: 1,657
Received 1 Upvote on 1 Post
Seems high, no? It's an apartment. Maybe I should turn everything on and then put a clamp meter round each leg to see what's really going through them?
 
 